FB_CTRL_nPOINT
FB_CTRL_nPOINT 1:
The function block provides an n-point transfer element in the functional diagram.
Behavior of the output
FB_CTRL_nPOINT 2:
Data array for the example:
FB_CTRL_nPOINT 3:
The value of the array with the index (1,1), i.e. the left value in the first row can be chosen freely, since it is not evaluated.
FB_CTRL_nPOINT 4: Inputs
    fSetpointValue    : FLOAT;
    fActualValue      : FLOAT;
    fManValue         : BOOL;
    eMode             : E_CTRL_MODE;
Type
fSetpointValue
FLOAT
Setpoint of the controlled variable
fActualValue
FLOAT
Actual value of the controlled variable
fManValue
Input whose value is output in manual mode.
eMode
E_CTRL_MODE
Input that specifies the operation mode of the function block.
FB_CTRL_nPOINT 5: Outputs
    fOut        : nPOINT_CTRL_TABLE_ELEMENT;
    eState      : E_CTRL_STATE;
    eErrorId    : E_CTRL_ERRORCODES;
    bError      : BOOL;
Type
fOut
nPOINT_CTRL_
TABLE_ELEMENT
Output of the n-point element
eState
E_CTRL_STATE
State of the function block
eErrorId
E_CTRL_ERRORCODES
Supplies the error number when the output bError is set.
Becomes TRUE, as soon as an error occurs.
FB_CTRL_nPOINT 6: Inputs/ outputs
    stParams    : ST_CTRL_nPOINT_PARAMS;
Type
stParams
Parameter structure of the n-point element
stParams consists of the following elements:
TYPE
ST_CTRL_nPOINT_PARAMS :
STRUCT
    tCtrlCycleTime           : TIME := T#0ms;
    tTaskCycleTime           : TIME := T#0ms;
    pDataTable_ADR           : POINTER TO nPOINT_CTRL_TABLE_ELEMENT
     := 0;
    nDataTable_SIZEOF        : UINT := 0;
    nDataTable_NumberOfRows  : UINT := 0;
    fHysteresisRange         : FLOAT;
END_STRUCT
END_TYPE
Type
tCtrlCycleTime
TIME
Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycle
Time
TIME
Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
pDataTable_
ADR
TABLE_
ELEMENT
Address of the data table
nDataTable_
SIZEOF
UINT
Size of the data table in bytes
nDataTable_
NumberOf
Rows
UINT
Number of rows in the data table
fHysteresis
Range
FLOAT
Hysteresis range, see diagram above. The hysteresis range functions as described for FB_CTRL_2POINT.