FB_CTRL_3POINT
FB_CTRL_3POINT 1:
The function block provides a 3-point transfer element in the functional diagram.
Behavior of the output
FB_CTRL_3POINT 2:
FB_CTRL_3POINT 3: Inputs
    fSetpointValue  : FLOAT;
    fActualValue    : FLOAT;
    nManSyncValue   : INT;
    bSync           : BOOL;
    eMode           : E_CTRL_MODE;
Type
fSetpointValue
FLOAT
Setpoint of the controlled variable
fActualValue
FLOAT
Actual value of the controlled variable
nManSyncValue
INT
Input with which the 3-point link can be set to one of the three junctions.
nManSyncValue >= 1 → bPosOut = TRUE,
bNegOut = FALSE
nManSyncValue <= -1 → bPosOut = FALSE, bNegOut = TRUE
otherwise → bPosOut = FALSE, bNegOut = FALSE
bSync
A rising edge at this input sets the 3-point element to the value "bManSyncValue".
eMode
E_CTRL_MODE
Input that specifies the operation mode of the function block.
FB_CTRL_3POINT 4: Outputs
    bPosOut    : BOOL;
    bNegOut    : BOOL;
    eState     : E_CTRL_STATE;
    eErrorId   : E_CTRL_ERRORCODES;
    bError     : BOOL;
Type
bPosOut
This output from the 3-point element is TRUE if the upper junction of the characteristic curve is active.
bNegOut
This output from the 3-point element is TRUE if the lower junction of the characteristic curve is active.
eState
E_CTRL_STATE
State of the function block
eErrorId
E_CTRL_ERRORCODES
Supplies the error number when the output bError is set.
Becomes TRUE, as soon as an error occurs.
FB_CTRL_3POINT 5: Inputs/ outputs
    stParams    : ST_CTRL_3POINT_PARAMS;
Type
stParams
Parameter structure of the 3-point element
stParams consists of the following elements:
TYPE
ST_CTRL_3POINT_PARAMS :
STRUCT
    tCtrlCycleTime    : TIME := T#0ms;
    tTaskCycleTime    : TIME := T#0ms;
    fPosOutOn         : FLOAT;
    fPosOutOff        : FLOAT;
    fNegOutOn         : FLOAT;
    fNegOutOff        : FLOAT;
END_STRUCT
END_TYPE
Type
tCtrlCycleTime
TIME
Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycle
Time
TIME
Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
fPosOutOn
FLOAT
Control deviation that will result in bPosOut = FALSE being switched to bPosOut = TRUE (bNegOut = FALSE).
fPosOutOff
FLOAT
Control deviation that will result in bPosOut = TRUE being switched to bPosOut = FALSE (bNegOut = FALSE).
fNegOutOn
FLOAT
Control deviation that will result in bNegOut = FALSE being switched to bNegOut = TRUE (bPosOut = FALSE).
fNegOutOff
FLOAT
Control deviation that will result in bNegOut = TRUE being switched to bNegOut = FALSE (bPosOut = FALSE).