FB_CTRL_TRANSFERFUNCTION_2
FB_CTRL_TRANSFERFUNCTION_2 1:
This function block calculates a discrete transfer function with the second standard form shown below. The transfer function here can be of any order, n.
The coefficients for the following transfer functions are stored in the parameter arrays:
FB_CTRL_TRANSFERFUNCTION_2 2:
Description of the transfer behavior
The internal calculation is performed in each sampling step according to the second standard form, for which the following block diagram applies:
FB_CTRL_TRANSFERFUNCTION_2 3:
The transfer function can be brought into the form shown in the block diagram by means of some transformations:
FB_CTRL_TRANSFERFUNCTION_2 4:
The coefficients of the counter polynomial are calculated according to the following rule:
FB_CTRL_TRANSFERFUNCTION_2 5:  FB_CTRL_TRANSFERFUNCTION_2 6:
FB_CTRL_TRANSFERFUNCTION_2 7:
The programmer must create the following arrays in the PLC if this function block is to be used:
aNumArray    : ARRAY[0..nTfOrder] OF FLOAT;
aDenArray    : ARRAY[0..nTfOrder] OF FLOAT;
aStTfData    : ARRAY[0..nTfOrder] OF ST_CTRL_TRANSFERFUNCTION_2_DATA;
The coefficients "b0" to "bn" are stored in the array aNumArray. This must be organized as follows:
aNumArray[0]:= b0;
aNumArray[1]:= b1;
aNumArray[n-1] := bn-1;
aNumArray[n] := bn;
The coefficients "a0" to "an" are stored in the array aDenArray. This must be organized as follows:
aDenArray[0]:= a0;
aDenArray[1]:= a1;
aDenArray[n-1] := an-1;
aDenArray[n] := an;
The internal data required by the function block is stored in the array aStTfData. This data must never be modified from within the PLC program. This procedure is also illustrated in the sample program listed below.
FB_CTRL_TRANSFERFUNCTION_2 8: Inputs
    fIn          : FLOAT;
    fManValue    : FLOAT;
    eMode        : E_CTRL_MODE;
Type
fIn
FLOAT
Input to the transfer function
fManValue
FLOAT
Input whose value is present at the output in manual mode.
eMode
E_CTRL_MODE
Input that specifies the operation mode of the function block.
FB_CTRL_TRANSFERFUNCTION_2 9: Outputs
    fOut        : FLOAT;
    eState      : E_CTRL_STATE;
    bError      : BOOL;
    eErrorId    : E_CTRL_ERRORCODES;
Type
fOut
FLOAT
Output from the transfer function
eState
E_CTRL_STATE
State of the function block
Supplies the error number when the output bError is set.
eErrorId
E_CTRL_ERRORCODES
Becomes TRUE, as soon as an error occurs.
FB_CTRL_TRANSFERFUNCTION_2 10: Inputs/ outputs
    stParams    : ST_CTRL_TRANSFERFUNCTION_2_PARAMS;
Type
stParams
Parameter structure of the function block
stParams consists of the following elements:
TYPE
ST_CTRL_TRANSFERFUNCTION_2_PARAMS:
STRUCT
    tTaskCycleTime                : TIME;
    tCtrlCycleTime                : TIME := T#0ms;
    nOrderOfTheTransferfunction   : USINT;
    pNumeratorArray_ADR           : POINTER TO FLOAT := 0;
    nNumeratorArray_SIZEOF        : UINT;
    pDenominatorArray_ADR         : POINTER TO FLOAT := 0;
    nDenomiantorArray_SIZEOF      : UINT;
    pTransferfunction2Data_ADR    : POINTER TO
    nTransferfunction2Data_SIZEOF : UINT;
END_STRUCT
END_TYPE
Type
tTaskCycleTime
TIME
Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
tCtrlCycleTime
TIME
Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
USINT
Order of the transfer function [0...]
pNumeratorArray_ADR
POINTER TO FLOAT
Address of the array containing the numerator coefficients
UINT
Size of the array containing the numerator coefficients, in bytes
POINTER TO FLOAT
Address of the array containing the denominator coefficients
UINT
Size of the array containing the denominator coefficients, in bytes
POINTER TO
ST_CTRL_
Address of the data array
UINT
Size of the data array in bytes
Sample:
PROGRAM PRG_TRANSFERFUNCTION_2_TEST
VAR CONSTANT
    nTfOrder : USINT := 2;
    bError              : BOOL;
    fbTansferfunction   : FB_CTRL_TRANSFERFUNCTION_2;
    bInit               : BOOL := TRUE;
    fIn                 : FLOAT := 0;
    fOut                : FLOAT;
    b_0, b_1, b_2       : FLOAT;
    a_0,a_1,a_2         : FLOAT;
IF bInit THEN
    aNumArray[0] := 1.24906304658218E-007;
    aNumArray[1] := 2.49812609316437E-007;
    aNumArray[2] := 1.24906304658218E-007;
    aDenArray[0] := 0.998501124344101;
    aDenArray[1] := -1.99850062471888;
    aDenArray[2] := 1.0;
    stParams.tTaskCycleTime    := T#2ms;
    stParams.tCtrlCycleTime    := T#2ms;
    stParams.nOrderOfTheTransferfunction := nTfOrder;
    eMode := eCTRL_MODE_ACTIVE;
    bInit := FALSE;
END_IF
stParams.pNumeratorArray_ADR := ADR(aNumArray);
stParams.nNumeratorArray_SIZEOF := SIZEOF(aNumArray);
stParams.pDenominatorArray_ADR := ADR(aDenArray );
stParams.nDenominatorArray_SIZEOF := SIZEOF(aDenArray );
stParams.pTransferfunction2Data_ADR := ADR(aStTfData );
stParams.nTransferfunction2Data_SIZEOF := SIZEOF(aStTfData);
fbTansferfunction (fIn := fIn,
                   eMode := eMode,
                   stParams := stParams,
                   fOut => fOut,
                   eErrorId => eErrorId,
                   bError => bError);