FB_CTRL_D
The function block provides a DT1 transfer element (a real D-element) in a functional diagram.
Transfer function (continuous)
fIn : FLOAT;
fManSyncValue : FLOAT;
bSync : BOOL;
eMode : E_CTRL_MODE;
Name | Type | Description |
fIn | FLOAT | Input of the D element |
fManSyncValue | FLOAT | Input to which the D-element can be synchronized, or whose value is present at the output in Manual Mode. |
bSync | BOOL | A rising edge at this input sets the D-element to the value "fManSyncValue". |
eMode | E_CTRL_MODE | Input that specifies the operation mode of the function block. |
Outputs
fOut : FLOAT;
eState : E_CTRL_STATE;
eErrorId : E_CTRL_ERRORCODES;
fOut | FLOAT | Output of the D element |
eState | E_CTRL_STATE | State of the function block |
eErrorId | E_CTRL_ERRORCODES | Supplies the error number when the output |
bError | BOOL | Becomes TRUE, as soon as an error occurs. |
Inputs/ outputs
stParams : ST_CTRL_D_PARAMS;
stParams | ST_CTRL_D_ | Parameter structure of the D-element |
stParams
consists of the following elements:
TYPE ST_CTRL_D_PARAMS:
STRUCT
tCtrlCycleTime : TIME := T#0ms;
tTaskCycleTime : TIME := T#0ms;
tTv : TIME := T#0ms;
tTd : TIME := T#0ms;
fOutMaxLimit : FLOAT := 1E38;
fOutMinLimit : FLOAT := -1E38;
END_STRUCT
END_TYPE
tCtrlCycleTime | TIME | Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle. |
tTaskCycleTime | TIME | Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task. |
tTv | TIME | Differentiation time constant |
tTd | TIME | Damping time constant |
fOutMaxLimit | FLOAT | Upper limit to which the output of the D-element is restricted. |
fOutMinLimit | FLOAT | Lower limit to which the output of the D-element is restricted. |
