FB_CTRL_LOOP_SCHEDULER
This function block allows the system load to be distributed over a number of control loops that are parameterized using the same tCtrlCycleTime and for which the condition "tCtrlCycleTime > tTaskCycleTime" is true. The output vector calculated by this function block is used to start the individual control loops at different times, so that the system loading is distributed.
Behavior of the output vector
5 control loops are managed in this diagram. In this case, "tCtrlCycleTime = 6 · tTaskCycleTime".
The programmer must create the following array in the PLC if this function block is to be used:
arrOutputVector : ARRAY[1..nNumberOfControlLoops] OF BOOL; The function block sets the bits in this vector to TRUE or FALSE. The control loops that are managed with the loop scheduler are to be switched into the eCTRL_MODE_ACTIVE state when the corresponding bit in the output vector is TRUE. See sample code below.
nManValue : DWORD;
eMode : E_CTRL_MODE;
nManValue | DWORD | This input allows the first 32 bits in the output vector to be set in |
eMode | E_CTRL_MODE | Input that specifies the operation mode of the function block. |
Outputs
eState : E_CTRL_STATE;
eErrorId : E_CTRL_ERRORCODES;
END_VAR Name | Type | Description |
eState | E_CTRL_STATE | State of the function block |
eErrorId | E_CTRL_ERRORCODES | Supplies the error number when the output |
bError | BOOL | Becomes TRUE, as soon as an error occurs. |
Inputs/ outputs
stParams : ST_CTRL_LOOP_SCHEDULER_PARAMS;
stParams | ST_CTRL_ | Parameter structure for the loop scheduler. |
stParams consists of the following elements:
TYPE
ST_CTRL_LOOP_SCHEDULER_PARAMS:
STRUCT
tCtrlCycleTime : TIME := T#0ms;
tTaskCycleTime : TIME := T#0ms;
nNumberOfControlLoops : UINT;
pOutputVector_ADR : POINTER TO BOOL := 0;
nOutputVector_SIZEOF : UINT := 0;
END_STRUCT
END_TYPE Name | Type | Description |
tCtrlCycleTime | TIME | The cycle time with which the control loops managed by the loop scheduler are processed. This must be greater than or equal to the TaskCycleTime. |
tTaskCycle | TIME | The cycle time with which the loop scheduler and the function blocks associated with the control loops are called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task. |
nNumberOfControlLoops | UINT | The number of control loops being managed. |
pOutputVector_ADR | POINTER TO BOOL | Address of the output vector |
nOutputVector_SIZEOF | UINT | Size of the output vector in bytes |
Sample:
PROGRAM PRG_LoopScheduler
arrOutputVector : ARRAY[1..5] OF BOOL;
fbCTRL_LoopScheduler : FB_CTRL_LOOP_SCHEDULER;
bInit : BOOL := TRUE;
eMode_CtrlLoop_1 : E_CTRL_MODE;
eMode_CtrlLoop_2 : E_CTRL_MODE;
eMode_CtrlLoop_3 : E_CTRL_MODE;
eMode_CtrlLoop_4 : E_CTRL_MODE;
eMode_CtrlLoop_5 : E_CTRL_MODE;
IF bInit
THEN
stParams.tCtrlCycleTime := T#10ms;
stParams.tTaskCycleTime := T#2ms;
stParams.nNumberOfControlLoops := 5;
bInit := FALSE;
END_IF
stParams.nOutputVector_SIZEOF := SIZEOF(arrOutputVector);
stParams.pOutputVector_ADR := ADR(arrOutputVector);
fbCTRL_LoopScheduler( eMode := eMode,
stParams := stParams,
eErrorId => eErrorId,
bError => bError);
IF arrOutputVector[1] THEN
eMode_CtrlLoop_1 := eCTRL_MODE_ACTIVE;
END_IF
IF arrOutputVector[2] THEN
eMode_CtrlLoop_2 := eCTRL_MODE_ACTIVE;
END_IF
IF arrOutputVector[3] THEN
eMode_CtrlLoop_3 := eCTRL_MODE_ACTIVE;
END_IF
IF arrOutputVector[4] THEN
eMode_CtrlLoop_4 := eCTRL_MODE_ACTIVE;
END_IF
IF arrOutputVector[5]
THEN
eMode_CtrlLoop_5 := eCTRL_MODE_ACTIVE;
END_IF