FB_PMA_PowerValues_1Ph
The function block FB_PMA_PowerValues_1Ph calculates the power values of the connected consumer. These include the fundamental components and the phase shift angle. Internally, the individual harmonics and their phase angle are determined for the calculations.
Alternatively, the function block FB_PMA_PowerValues_Period_1Ph can be used for the calculation. It uses simpler calculation methods for enhanced dynamics.
The input buffer is provided via the function block FB_PMA_Source_1Ph. The size of the input buffer is half the window length.
By way of example, possible FFT and window lengths are shown in the following table:
FFT length | Window length | Buffer length | |
512 | 29 | 400 | 200 |
1024 | 210 | 800 | 400 |
2048 | 211 | 1600 | 800 |
4096 | 212 | 3200 | 1600 |
8192 | 213 | 6400 | 3200 |
16384 | 214 | 12800 | 6400 |
Memory properties
Since the Welch method is used, in each case the current input buffer together with the last transferred buffer is used for the calculation.
The frequency analysis takes step changes in the time series into account. In order to achieve a correct result, the last two input buffers should therefore be consecutive without step changes.
Definition:
FUNCTION BLOCK FB_PMA_PowerValues_1Ph
nOwnID : UDINT;
tTransferTimeout : LTIME := LTIME#500US;
stInitPars : ST_PMA_PowerValues_InitPars;
bNewResult : BOOL;
nCntResults : ULINT;
fApparentPower : LREAL;
fApparentPower_1 : LREAL;
fApparentPower_1_Min : LREAL;
fApparentPower_1_Max : LREAL;
fActivePower : LREAL;
fActivePower_Min : LREAL;
fActivePower_Max : LREAL;
fReactivePower_d : LREAL;
fReactivePower_1 : LREAL;
fReactivePower_1_Min : LREAL;
fReactivePower_1_Max : LREAL;
fTotalReactivePower : LREAL;
fPhi : LREAL;
fCosPhi : LREAL;
fPowerFactor : LREAL;
bValidStatistics : BOOL;
VAR_OUTPUT PERSISTENT
stEnergy_Pos : ST_PMA_Energy;
stEnergy_Neg : ST_PMA_Energy;
stEnergy_Res : ST_PMA_Energy;
The input parameters of this function block represent initialization parameters and must be assigned when declaring the function block instance (alternative: Init method). They may only be assigned once. A change at runtime is not possible.
Name | Type | Description |
nOwnID | UDINT | Identifies the function block instance with a unique ID. This must always be greater than zero. A proven approach is to define an enumeration for this purpose. |
tTransferTimeout | LTIME | Setting of the synchronous timeout for internal multi-array forwardings. See Parallel Processing in Transfer Tray. |
stInitPars | Function-block-specific structure with initialization parameters. The parameters must match the definition of the input and output buffers. |
Outputs
bError | BOOL | TRUE if an error occurs. |
ipResultMessage | I_TcMessage | The interface offers detailed information about the return value. |
bNewResult | BOOL | TRUE once new results have been calculated. |
nCntResults | ULINT | Count value is incremented with new output data. |
fApparentPower | LREAL | Total apparent power |
fApparentPower_1 | LREAL | Fundamental apparent power |
fApparentPower_1_Min | LREAL | Smallest value of fApparentPower_1 that has occurred. Can be reset via bResetStatistics of the Call method. |
fApparentPower_1_Max | LREAL | Largest value of fApparentPower_1 that has occurred. Can be reset via bResetStatistics of the Call method. |
fActivePower | LREAL | Active power |
fActivePower_Min | LREAL | Smallest value of fActivePower that has occurred. Can be reset via bResetStatistics of the Call method. |
fActivePower_Max | LREAL | Largest value of fActivePower that has occurred. Can be reset via bResetStatistics of the Call method. |
fReactivePower_d | LREAL | Distortion reactive power |
fReactivePower_1 | LREAL | Fundamental shift reactive power |
fReactivePower_1_Min | LREAL | Smallest value of fReactivePower_1 that has occurred. Can be reset via bResetStatistics of the Call method. |
fReactivePower_1_Max | LREAL | Largest value of fReactivePower_1 that has occurred. Can be reset via bResetStatistics of the Call method. |
fTotalReactivePower | LREAL | Total reactive power |
fPhi | LREAL | Phase shift angle |
fCosPhi | LREAL | CosPhi (active power/fundamental apparent power) |
fPowerFactor | LREAL | Power factor (active power/total apparent power) |
bValidStatistics | BOOL | TRUE if the Min and Max value calculation has been performed. These values are valid. |
stEnergy_Pos | Energy in positive direction. The output is saved persistently and can be reset via bResetEnergyCalc of the Call method. | |
stEnergy_Neg | Energy in negative direction. The output is saved persistently and can be reset via bResetEnergyCalc of the Call method. | |
stEnergy_Res | Resulting energy. The output is saved persistently and can be reset via bResetEnergyCalc of the Call method. |
Methods
Name | Description |
The method is called in each cycle to execute the calculations from the input buffer when new data is present. | |
Alternative to the function block initialization | |
As an alternative to the Call method, the method can be called in each cycle if no calculation is to take place. The incoming input buffer is then forwarded accordingly. | |
The method is called in order to reconfigure the function block during the runtime. | |
This method deletes all the data sets already added. In addition, the calculated output values are reset. |
Sample
VAR CONSTANT
cOversamples : UDINT := 10;
cFFT_Length : UDINT := 4096;
cWindowLength : UDINT := 3200;
cSourceInitPars: ST_PMA_Source_InitPars := (
nBufferLength := cWindowLength/2);
cPowerValuesInitPars : ST_PMA_PowerValues_InitPars := (
nFFT_Length := cFFT_Length,
nWindowLength := cWindowLength,
fSampleRate := cOversamples * 1000,
fBaseFreq := 50.0,
nNumBands := 40,
fBandwidth := 20.0,
eWindowType := E_PMA_WindowType.HannWindow,
fTimeLagCurrentTransformer := 0.0,
fMinInputCurrent := 0.01);
aVoltage AT%I* : ARRAY[1..cOversamples] OF LREAL;
aCurrent AT%I* : ARRAY[1..cOversamples] OF LREAL;
fbSource : FB_PMA_Source_1Ph := (nOwnID := 1, aDestIDs := [2], stInitPars := cSourceInitPars);
fbPowerValues : FB_PMA_PowerValues_1Ph := (nOwnID := 2, stInitPars := cPowerValuesInitPars);
END_VAR// Call source
fbSource.Call(ADR(aVoltage), ADR(aCurrent), SIZEOF(aVoltage), 0);
// Call algorithm
fbPowerValues.Call(FALSE, FALSE);Requirements
TwinCAT v3.1.4024.0 | PC or CX (x86, x64) | Tc3_PowerMonitoring |
