FB_PMA_Frequency_Period_3Ph
The function block FB_PMA_Frequency_Period_3Ph calculates the base frequency of the given input signal for all three phases. To do this, the signal is first filtered with a Butterworth low-pass filter. The zero crossings of the input signal are then determined from the filtered values, and the frequency is calculated from their difference. The results refer to one or more periods, depending on the configuration. The statistical results refer to the entire runtime or the time at which the statistical results were last reset.
The input buffer is provided via the function block FB_PMA_Source_3Ph. This can include one or more signal periods or individual fragments of oversampling arrays.
Definition:
FUNCTION BLOCK FB_PMA_Frequency_Period_3Ph
nOwnID : UDINT;
tTransferTimeout : LTIME := LTIME#500US;
stInitPars : ST_PMA_Frequency_Period_InitPars;
bNewResult : BOOL;
nCntResults : ULINT;
aFreq : ARRAY[0..2] OF LREAL;
aFreq_Min : ARRAY[0..2] OF LREAL;
aFreq_Max : ARRAY[0..2] OF LREAL;
aRocof : ARRAY[0..2] OF LREAL;
eRotDirection : E_PMA_RotationalDirection_3Ph;
bValidStatistics : BOOL;
aOutOfRange : ARRAY[0..2] OF BOOL;
The input parameters of this function block represent initialization parameters and must be assigned when declaring the function block instance (alternative: Init method). They may only be assigned once. A change at runtime is not possible.
Name | Type | Description |
nOwnID | UDINT | Identifies the function block instance with a unique ID. This must always be greater than zero. A proven approach is to define an enumeration for this purpose. |
tTransferTimeout | LTIME | Setting of the synchronous timeout for internal multi-array forwardings. See Parallel Processing in Transfer Tray. |
stInitPars | Function-block-specific structure with initialization parameters. The parameters must correlate to the above definition of the input and output buffers. |
Outputs
bError | BOOL | TRUE if an error occurs. |
ipResultMessage | I_TcMessage | The interface offers detailed information about the return value. |
bNewResult | BOOL | TRUE once new results have been calculated. |
nCntResults | ULINT | Count value is incremented with new output data. |
aFreq | ARRAY[0..2] OF LREAL | Frequency determined by two or more zero crossings. |
aFreq_Min | ARRAY[0..2] OF LREAL | Smallest value of fFreq that has occurred. Can be reset via bResetStatistics of the Call method. |
aFreq_Max | ARRAY[0..2] OF LREAL | Largest value of fFreq that has occurred. Can be reset via bResetStatistics of the Call method. |
aRocof | ARRAY[0..2] OF LREAL | Rate of change of frequency (ROCOF) |
eRotDirection | Direction of rotation | |
bValidStatistics | BOOL | TRUE if the Min and Max value calculation has been performed. These values are valid. |
aOutOfRange | ARRAY[0..2] OF | TRUE as soon as the input value or the frequency is not within the configured limits. |
Methods
Name | Description |
The method is called in each cycle to execute the calculations from the input buffer when new data is present. | |
Alternative to the function block initialization | |
As an alternative to the Call method, the method can be called in each cycle if no calculation is to take place. The incoming input buffer is then forwarded accordingly. | |
The method is called in order to reconfigure the function block during the runtime. | |
The current calculations are reset with the method. |
Sample
VAR CONSTANT
cOversamples : UDINT := 10;
cSourceInitPars: ST_PMA_Source_InitPars := (
nBufferLength := cOversamples);
cFrequencyInitPars : ST_PMA_Frequency_Period_InitPars := (
nBufferLength := cOversamples,
fSampleRate := cOversamples * 1000,
fMinFreq := 45.0,
fMaxFreq := 55.0,
nPeriods := 1,
nFilterOrder := 2,
fCutOff := 70.0,
eInputSelect := E_PMA_InputSelect.Voltage,
fMinInput := 200.0);
aVoltage AT%I* : ARRAY [0..2] OF ARRAY[1..cOversamples] OF LREAL;
aCurrent AT%I* : ARRAY [0..2] OF ARRAY[1..cOversamples] OF LREAL;
fbSource : FB_PMA_Source_3Ph := (nOwnID := 1, aDestIDs := [2], stInitPars := cSourceInitPars);
fbFrequency : FB_PMA_Frequency_Period_3Ph := (nOwnID := 2, stInitPars := cFrequencyInitPars);
END_VAR// Call source
fbSource.Call(
ADR(aVoltage[0]),
ADR(aVoltage[1]),
ADR(aVoltage[2]),
ADR(aCurrent[0]),
ADR(aCurrent[1]),
ADR(aCurrent[2]),
SIZEOF(aVoltage[0]),
0);
// Call algorithms
fbFrequency.Call(FALSE);Requirements
TwinCAT v3.1.4024.0 | PC or CX (x86, x64) | Tc3_PowerMonitoring |