FB_CMA_VibrationAssessment
Vibration assessment of real-valued input signals.
The function block FB_CMA_VibrationAssessment performs a vibration assessment of real-valued input signals on the basis of ISO 10816-3. This is explained in more detail in the section Application concepts, see Vibration assessment. The function block combines the calculation of integrated RMS values on configurable frequency bands with their classification for single and multi-channel input data.
The result is a one-dimensional array that contains three values for each frequency band: the highest calculated classification (in the range -1..nMaxClasses), the associated integration order (in the range 0..nOrder) and the channel (in the range 1..nChannels). It is recommended to save the result of the classification on the Sink in a two-dimensional array in the form aResult : ARRAY[1..nMaxBands] OF ARRAY [1..3] OF DINT. The data are then available for each band as follows: [{class},{order},{channel}].
The data contained can be used to make a statement/evaluation with regard to the machine state on the basis of the vibration measurements. The possible configuration of several frequency bands facilitates the evaluation; the condition for various speeds of the machine can be determined simultaneously taking the example of the ISO 10816-3.
![]() | Note the window length The value of |
If nFFT_Length is greater than nWindowLength, the frequency resolution of the FFT (and therefore also the length of the return values vector) is increased. The length difference is filled with zeros before the Fourier transform. This can be useful for achieving a higher frequency resolution, or for avoiding circular aliasing in calculations with inverse transformation in the time domain. Despite the higher frequency resolution, however, the result contains no more information.
Memory properties
Due to the use of the Welch method, the current input data buffer, together with the last-transferred buffers, is used for the calculation. The number of buffers incorporated depends on the selected overlap (nOverlap).
The frequency analysis takes step changes in the time series into account. In order to achieve a correct result, therefore, the input data buffers used must be concatenated without gaps and without jumps.
Behavior when processing multi-channel input data
When processing several channels (nChannels > 1), there is a possibility of each channel having different return values. In this case, return values can be queried separately on the function block. If the results from one or more channels are impermissible, but not all channels, the value on the function block corresponds to eCM_InfRTime_AmbiguousChannelResults. If the results of all channels are impermissible, then the value on the function block corresponds to eCM_ErrRTime_ErrornousChannelResults.
A list of return values of all channels can be queried using the method GetChannelErrors().
Sample implementation
A sample implementation is available under the following link: Vibration assessment according to ISO 10816-3 (compact).
Inputs and outputs
The input and output buffers correspond to one of the following definitions (input / output shape). The variable parameters are part of the function block input stInitPars.
Versions | Input buffer (MultiArray input stream) | Output buffer (MultiArray output stream) |
Standard version |
Multi-channel version |
stInitPars : ST_CM_VibrationAssessment_InitPars; // init parameter
nOwnID : UDINT; // ID for this FB instance
aDestIDs : ARRAY[1..cCMA_MaxDest] OF UDINT; // IDs of destinations for output
nResultBuffers : UDINT := 4; // number of MultiArrays which should be initialized for results (0 for no initialization)
tTransferTimeout : LTIME := LTIME#500US; // timeout checking off during access to inter-task FIFOs
END_VARInput parameters
The input parameters of this function block represent initialization parameters and must already be assigned in the declaration of the FB instance! (Alternatively: Init() method). They may only be assigned once. A change at runtime is not possible.
stInitPars: Function-block-specific structure with initialization parameters of the type ST_CM_VibrationAssessment_InitPars. The parameters must correlate to the above definition of the input and output buffers.nOwnID: Identifies the function block instance with a unique ID. This must always be greater than zero. A proven approach is to define an enumeration for this purpose.aDestIDs: Defines the destinations to which the results are to be forwarded by specifying the IDs of the destinations. The definition of the output buffer (as described above) must correlate to the definition of the input buffer of each selected destination.nResultBuffers: The function block initializes a Transfer Tray Stream with the specified number of MultiArray buffers. The default value is four.tTransferTimeout: Setting of the synchronous timeout for internal MultiArray forwardings. See section Parallel processing.
Output parameters
bError : BOOL; // TRUE if an error occurs. Reset by next method call.
hrErrorCode : HRESULT; // '< 0' = error; '> 0' = info; '0' = no error/info
ipErrorMessage : I_TcMessage := fbErrorMessage; // Shows detailed information about occurred errors, warnings and more.
nCntResults : ULINT; // Counts outgoing results (MultiArrays were calculated and sent to transfer tray).
END_VAR-
bError: The output isTRUEif an error occurs. -
hrErrorCode: If an error occurs, a corresponding error code of the typeHRESULTis output. Possible values are described in the List of error codes. -
ipErrorMessage: Contains more detailed information on the current return value. Refer here to the section Error description and information. This special interface pointer is internally secured so that it is always valid/assigned.
Methods
METHOD Init : HRESULT
END_VARCall():
The method is called each cycle in order to apply the algorithm to the current input data. The function block waits for input data if the method indicates neither new results nor an error. This is a regular behavior in the process of the analysis chain.
- Return value: If an error occurs, a corresponding error code of the type
METHOD Call : HRESULT
bNewResult : BOOL; // TRUE every time when outgoing MultiArray was calculated and sent to transfer tray.
END_VARbError: The output isTRUEif an error occurs.hrErrorCode: If an error occurs, a corresponding error code of the typeHRESULTis output. Possible values are described in the List of error codes. This output is identical to the return value of the method.
![]() | If a timeout occurs or no MultiArray buffer is available for the result, then neither the input data nor the result data are lost. They are forwarded on the next call. |
Init():
This method is not usually necessary in a Condition Monitoring application. It offers an alternative to the function block initialization. The Init() method may only be called during the initialization phase of the PLC. It cannot be used at runtime. You are referred to the use of an FB_init method or the attribute 'call_after_init' (see TwinCAT PLC reference). In addition, this facilitates the function block encapsulation.
The input parameters of the function block instance may not be assigned in the declaration if the initialization is to take place using the Init() method.
Configure():
On calling this method, the classification arguments and frequency bands must be configured at the beginning. The corresponding PLC arrays must be defined as follows. The Configure() method can also be used for a new configuration with a different set of arguments.
METHOD Configure : HRESULT
pArg1 : POINTER TO LREAL; // pointer to 2-dimensional array (LREAL) of arguments for classification
nArgSize1 : UDINT; // size of arguments buffer in bytes
pArg2 : POINTER TO LREAL; // pointer to 2-dimensional array (LREAL) of arguments for frequency bands
nArgSize2 : UDINT; // size of arguments buffer in bytes
END_VARThe input buffers correspond to one of the following definitions (input shape). The variable parameters are part of the function block input stInitPars. The two parameters to be configured per frequency band are [fLowerFrequencyLimit, fUpperFrequencyLimit] (input buffer 2).
Versions | Input buffer 1 (MultiArray input stream) | Input buffer 2 (MultiArray input stream) |
Identical configuration of all channels |
ResetData():
The method deletes all data records that have already been added, see Memory property of the function block. If the Call() method is called again after a ResetData(), the internal memory must be replenished in order to calculate a valid result.
METHOD ResetData : HRESULT
END_VARPassInputs():
As long as an FB_CMA_Source instance is called and signal data are thus transferred to a target block, all further function blocks of the analysis chain have to be called cyclically as explained in the API PLC Reference.
Sometimes it is useful not to execute an algorithm for a certain time. For example, some algorithms should be executed only after prior training or configuration. The function block must be called cyclically, but it is sufficient for the data arriving at the function block to be forwarded in the communication ring. This is done using the PassInputs() method in place of the Call() method. The algorithm itself is not called here, and accordingly no result is calculated and no output buffer generated.
METHOD PassInputs : HRESULT
END_VARGetChannelErrors():
The method enables the querying of a list of the channel-specific return values when processing several channels (nChannels > 1). A call is useful in the case that the return value of the function block corresponds to one of the values eCM_InfRTime_AmbiguousChannelResults or eCM_ErrRTime_ErrornousChannelResults.
Return value: Information on the reading process of the list of error codes. The value is set to
TRUEif the query was successful, otherwise toFALSE.
METHOD GetChannelErrors : BOOL
aChannelErrors : ARRAY[*] OF HRESULT;
aChannelErrors: Error list of the typeHRESULTof the lengthnChannels.
Similar function blocks
The function block FB_CMA_IntegratedRMS calculates (optionally) integrated RMS values for single and multi-channel real-valued time series.
The function block FB_CMA_WatchUpperThresholds performs the configurable threshold value monitoring of multi-channel data.
TwinCAT v3.1.4022.25 | PC or CX (x86, x64) | Tc3_CM, Tc3_CM_Base |
![]() | Limited functional scope already available with CM 3.1. See section Compatibility. |