FB_ALY_Mean_1Ch
The Mean 1Ch calculates the mean value over the input values according to the formula
FB_ALY_Mean_1Ch 1:
The number of samples N that are included in the calculation can be configured by specifying a time interval. A cascaded output can be configured to realize a long-term mean value in a resource-saving way and to pick up intermediate results. The time interval of the configured cascade must correspond to an integer multiple of the time interval of the previous cascade.
Definition:
FUNCTION_BLOCK FB_ALY_Mean_1Ch
    ipResultMessage: Tc3_EventLogger.I_TcMessage;
    bError: BOOL;
    bNewResult: BOOL;
    bConfigured: BOOL;
FB_ALY_Mean_1Ch 2: Outputs
Type
ipResultMessage
I_TcMessage
Contains more detailed information on the current return value. This special interface pointer is internally secured so that it is always valid/assigned.
This output is TRUE if an error occurs.
bNewResult
When a new result has been calculated, the output is TRUE.
bConfigured
Displays TRUE when the function block is successfully configured.
FB_ALY_Mean_1Ch 3: Methods
Definition location
Call()
Local
Method for calculating the outputs for a specific configuration.
Configure()
Local
General configuration of the algorithm with its parameterized conditions.
SetCascades()
Local
Method for configuring the cascades. The call is made after the call to the Configure method.
Reset()
Local
Resets all internal states or the calculations performed so far.
SetChannelValue()
Local
Method for passing values to the algorithm.
Sample
    fbMean : FB_ALY_Mean_1Ch;
    fbSystemTime : FB_ALY_GetSystemTime;
    nNumCascades : UDINT := 5;
    fSampleRate : UDINT := 1000;
    eStartupBehaviour : E_ALY_CascadeStartupBehaviour := E_ALY_CascadeStartupBehaviour.UsePreviousCascadeValue;
    aCascadesConfigArray : ARRAY[1..5] OF LTIME := [LTIME#20MS, LTIME#1S, LTIME#1M, LTIME#1H, LTIME#1D];
    bConfigure : BOOL := TRUE;
    fInput : LREAL;
    aMean : ARRAY[1..5] OF LREAL;
    aNewResult : ARRAY[1..5] OF BOOL;
// Configure algorithm
IF bConfigure THEN
    bConfigure := FALSE;
    fbMean.Configure(nNumCascades, fSampleRate, eStartupBehaviour);
    fbMean.SetCascades(ADR(aCascadesConfigArray), SIZEOF(aCascadesConfigArray));
END_IF
// Get current system time
fbSystemTime.Call();
// Call algorithm
fbMean.SetChannelValue(fInput);
fbMean.Call(fbSystemTime.tSystemTime, ADR(aMean), SIZEOF(aMean), ADR(aNewResult), SIZEOF(aNewResult))
Development environment
Target platform
Plc libraries to include
TwinCAT v3.1.4024.0
PC or CX (x64, x86)
Tc3_Analytics