FB_ALY_StepResponse_1Ch
Step Response 1Ch identifies parameters of the step response of a PT2 track. These include the delay time Te, the compensation time Tb, the settling time Tcs, and the time of maximum tm.
![FB_ALY_StepResponse_1Ch 1:](Images/png/13575777419__Web.png)
To detect whether the track is steady, a local minimum or maximum is searched for. If this is within the tolerance band (marked in gray), it is assumed that the track is steady. Only then is the settling time set.
The algorithm starts when a new setpoint is outside the previously stored tolerance band.
Definition:
FUNCTION_BLOCK FB_ALY_StepResponse_1Ch
ipResultMessage: Tc3_EventLogger.I_TcMessage;
bError: BOOL;
bNewResult: BOOL;
bConfigured: BOOL;
bExecuting: BOOL;
fbEquivalentDeadTime: FB_ALY_Timespan;
fbEquivalentTimeConstant: FB_ALY_Timespan;
fbSettlingTime: FB_ALY_Timespan;
fbTimeMax: FB_ALY_DateTime;
fError: LREAL;
Outputs
Name | Type | Description |
ipResultMessage | Contains more detailed information on the current return value. This special interface pointer is internally secured so that it is always valid/assigned. | |
bError | BOOL | This output is |
bNewResult | BOOL | When a new result has been calculated, the output is |
bConfigured | BOOL | Displays |
bExecuting | BOOL |
fbEquivalentDeadTime | FB_ALY_Timespan | Delay time of the track. Timespan between the start of the step response and the intersection of the inflectional tangents with the start value. |
fbEquivalentTimeConstant | FB_ALY_Timespan | Compensation time of the track. Timespan between the intersection point of the inflectional tangents with the start value and the intersection point of the inflectional tangents with the setpoint. |
fbSettlingTime | FB_ALY_Timespan | Settling time of the track. |
fbTimeMax | FB_ALY_DateTime | Time of the maximum overshoot. |
fError | LREAL | Difference between input value and setpoint. |
Methods
Name | Definition location | Description |
Call() | Local | Method for calculating the outputs for a specific configuration. |
Configure() | Local | General configuration of the algorithm with its parameterized conditions. |
Reset() | Local | Resets all internal states or the calculations performed so far. |
SetChannelValue() | Local | Method for passing values to the algorithm. |
Sample
fbStepResponse : FB_ALY_StepResponse_1Ch;
fbSystemTime : FB_ALY_GetSystemTime;
fThresholdReversal : LREAL;
bUseRelativeTolerance : BOOL;
fErrorTolerance : LREAL;
bConfigure : BOOL := TRUE;
fInput : LREAL;
fSetpoint : LREAL;
// Get current system time
fbSystemTime.Call();
// Configure algorithm
IF bConfigure THEN
bConfigure := FALSE;
fbStepResponse.Configure(fThresholdReversal, bUseRelativeTolerance, fErrorTolerance);
END_IF
// Call algorithm
fbStepResponse.SetChannelValue(1, fInput);
fbStepResponse.SetChannelValue(2, fSetpoint);
fbStepResponse.Call(fbSystemTime.tSystemTime)
Development environment | Target platform | Plc libraries to include |
TwinCAT v3.1.4024.0 | PC or CX (x64, x86) | Tc3_Analytics |
