Timing Analysis 1Ch
The Timing Analysis 1Ch measures time differences between on- and off-periods and counts the amount of on-periods. The on-period starts when the condition of operator and threshold is met.
Configuration options
- Operator: Specifies whether the input value should be greater than, greater than or equal to, less than or equal to, less than or not equal to the threshold.
- Threshold: Signal threshold.
- Tolerance (optional): Tolerance value for the Equal / NotEqual comparisons.
Output Values
- Is On: Shows TRUE within the time range of the on-period, otherwise FALSE.
- Current Interval: Shows the time of the current interval.
- On Total: Shows the total time the "Is On"-value is TRUE.
- Off Total: Shows the total time the "Is On"-value is FALSE.
- Count On: Counts the amount of raised on-events.
Standard HMI Controls
For the Timing Analysis 1Ch algorithm, the following HMI controls are available for generating an Analytics Dashboard:
1. The TimingAnalysis Control visualizes the output values Is On, On Total, Off Total and Current Interval.
2. The SingleValue control visualizes the output value Count On.
3. The Table Control or Multivalue Control visualizes all output values: Is On, Count On, Current Interval, On Total, Off Total.
Alternatively, customer-specific HMI controls can be mapped in the Timing Analysis 1Ch algorithm using the Mapping Wizard.