DCF77_TIME
The "DCF77_TIME" function block can be used to decode the DCF-77 radio clock signal.
![]() | This function block is replaced by the new "DCF77_TIME_EX" function block. |
A rising edge at the RUN input starts the decoding process, which continues as long as the RUN input remains set. In the worst case, the function block requires a maximum of 1 minute to synchronize itself, plus a further minute to decode the data for the following minute. During this time, the missing 59th second marker is waited for. Internally the function block is sampling the DCF-77 signal. In order to be able to sample the edges without error the function block should be called once in each PLC cycle. Satisfactory results can be obtained with a cycle time of <= 25 ms. In case of a missing or faulty DCF-77 signal, the ERR output is set to TRUE and a corresponding error code is set at the ERRID output. The ERR and ERRID outputs are reset the next time a correct signal is received. Some receivers provide an inverted DCF-77 signal. In such cases the signal must first be inverted before being passed to the DCF_PULSE input. When operating without errors, the current time is updated at the CDT output every minute. Thereby the READY output is set to TRUE for one cycle of the PLC at the zeroth second. At this time the DCF-77 time at the CDT output is valid, and can be evaluated by the PLC program. The READY output is only set if no error was detected in the data for the following minute. The transferred parity bits are used for error detection. In the event of poor reception conditions, 100% error-free detection cannot be guaranteed. I.e. with two faulty (inverted) bits, the function block cannot detect an error and also sets the READY output to TRUE. In order to obtain reliable time information additional safeguards have to be implemented, e.g. redundancy analysis of the time information in consecutive minutes.
From TwinCAT v2.10 Build > 1340 and TwinCAT v2.11 Build > 1542 a simple plausibility check of two consecutive telegrams was implemented in the DCF77_TIME function block. This functionality can be activated via a global Boolean variable for all instances of the DCF77_TIME block. When the plausibility check is activated the first synchronization is extended by a further minute to a maximum of 3 minutes.
GLOBAL_DCF77_SEQUENCE_CHECK : BOOL := FALSE;(* TRUE = Enable plausibility check (two telegrams are checked), FALSE = Disable check *)
Errors that occur during reception are registered by the function block. The ERRCNT output is an error counter. This counter indicates the number of errors that have occurred since the last correctly received signal. The counter is reset the next time a signal is correctly received.
Time code
During each minute, the numbers that encode the year, month, day, day of the week, hour and minute are transmitted in BCD format through pulse modulation of the second marks. The transmitted information always describes the subsequent minute. A second marker is transmitted each second. A second marker with a duration of 0.1 s represents a binary zero, while a duration of 0.2 s represents binary one. The information is extended with 3 check bits. No second marker is transmitted for the 59th second, and a receiver can use this "gap" to synchronize itself.
From TwinCAT v2.10 Build > 1340 and TwinCAT v2.11 Build > 1542 the length of the short and long pulse signal can also be configured via a global variable. If the signal is poor the pulse widths are smaller. The receiver specification usually contains information about the minimum and maximum pulse for the two logic signals, with the higher value expected for higher field strengths and the lower value for low field strengths or in the event of interference. Problems may also occur near the sender (where the field strength is very large) if the pulse width of the logic zero becomes excessive. For this reason a fixed limit is set for differentiating between zero and one, depending on the receiver specification. Check the specification of the receiver used and configure the pulse length accordingly.
GLOBAL_DCF77_PULSE_SPLIT : TIME := T#140ms;(* 0 == pulse < 140ms, 1 == pulse > 140 *)
E.g.: in the specification of Atmel T4227 (Time Code Receiver) the following pulse length is given:
100ms pulse (zero): min: 70ms, typical: 95ms, max: 130ms
200ms pulse (one): min 170ms, typical 195ms, max 235ms
For this IC a limit value of 150ms would be optimal = 130 + ( ( 170ms - 130ms ) / 2 ).
![]() | If the configured limit value for the pulse length is too small, short pulses are detected as long. Conversely, if the configured limit value is too small, long pulses are detected as short. If the checksum is correct, the receiver cannot detect these errors. In the first case the receiver may supply times that are in future range, in the second case the times may be in the past. |
DCF_PULSE :BOOL;
RUN :BOOL;
END_VARDCF_PULSE: the DCF-77 signal.
RUN: a rising edge at this input initializes the function block and starts decoding the DCF-77 signal. If this input is reset, the decoding process is stopped.
BUSY :BOOL;
ERR :BOOL;
ERRID :UDINT;
ERRCNT :UDINT;
READY :BOOL;
CDT :DATE_AND_TIME;
END_VARBUSY: when the function block is activated, this output is set.
ERR: if an error occurred during decoding, this output is set.
ERRID: supplies the error number when the ERR output is set.
ERRCNT: number of errors that have occurred since the last error-free reception.
READY: if this output is set, then the data at the CDT output are valid.
CDT: the DCF-77 time in DATE_AND_TIME format.
Error description:
Error Codes | Error description |
0 | No error |
0x100 | Timeout error. Possibly no DCF-77 signal detected. |
0x200 | Parity error. Incorrect bits were detected in the received data. |
0x300 | Faulty data received. Since the parity check can only detect one incorrect bit, the received data are checked again for validity (this error code will be generated, for instance, if month = 13). |
0x400 | The last decoding cycle was too long. This error can occur when reception is poor (not enough second markers were received). |
0x500 | The last decoding cycle was too short. This error can occur when reception is poor (additional edges were received). |
Example of a call in FBD
In the example application, the Real Time Clock is synchronized with the radio time in case of an error-free reception.
TwinCAT v2.10.0 Build > 1313 and higher | PC or CX (x86, ARM) | TcUtilities.Lib |