FB_TempController
The temperature controller function block FB_TempController has a variety of inputs and outputs that are described below. All the controller's parameters are passed to it via structures. The structures and enums are defined here.
Function block
Interface
bOn : BOOL; (* start closed loop operating *)
bInit : BOOL; (* init controller *)
bTune : BOOL; (* start self tuning *)
bManual : BOOL; (* manual operation *)
bSelSetpoint : BOOL; (* FALSE = setpoint 1, TRUE = setpoint 2
bSelCtrlParameterSet : BOOL; (* FALSE = internal set, TRUE =
external set *)
bEnableSoftStart : BOOL; (* FALSE = no soft start, TRUE = soft
start *)
bEnableRamping : BOOL; (* FALSE = no ramping, TRUE = ramping
fW1 : LREAL; (* first setpoint *)
fW2 : LREAL; (* second setpoint *)
fX : LREAL; (* actual value *)
(* alarming inputs *)
bOpenThermocouple : BOOL; (* thermocouple *)
bReverseThermocouple : BOOL;
bBackVoltage : BOOL;
bLeakage : BOOL; (* heating system *)
bShortCircuit : BOOL;
bOpenCircuit : BOOL;
sParaControllerExternal : ST_ParaController; (* external
controller parameter set *)
(* logging *)
sLogData : ST_LogData := (bLog := FALSE, strLogFileName :=
'', strLogString := '' );
sControllerParameter : ST_ControllerParameter; (* parameters
fYAnalog : LREAL; (* control value analog *)
bYPWM : BOOL; (* control value PWM *)
bYDig : BOOL; (* 2-Point *)
bYDigPos : BOOL; (* 3-Point: control value digital positive
bYDigNeg : BOOL; (* 3-Point: control value digital
negative*)
(* alarming *)
dwAlarm : DWORD; (* max. 32 alarms *)
(* state *)
iState : States := TC_STATE_IDLE;
(* controller parameter *)
sParaControllerInternal : ST_ParaController;
(* general errors *)
iErrorId : ErrorCodes;
Name | Unit | Value range | Description |
bOn | 1 | [TRUE,FALSE] | TRUE switches the controller on. |
bInit | 1 | [TRUE,FALSE] | Initialization flag, which must be active (TRUE) for precisely the first cycle in which the controller is called. |
bTune | 1 | [TRUE,FALSE] | A rising edge switches the self-tuning on. If it is switched to FALSE during the self-tuning process then the self-tuning is aborted and the controller continues operation using the old parameters (if they are still present). |
bManual | 1 | [TRUE,FALSE] | TRUE switches manual operation on. If the signal goes FALSE again, the controller returns to automatic mode. |
bSelSetpoint | 1 | [TRUE,FALSE] | Selects one of two possible setpoints. FALSE selects the normal setpoint, while TRUE selects the standby setpoint. |
bSelCtrlParameterSet | 1 | [TRUE,FALSE] | Selects one of two parameter sets. FALSE causes the internal (determined) parameter set to be used, while TRUE switches to one provided externally. |
bEnableSoftStart | 1 | [TRUE,FALSE] | The soft start-up process is used if TRUE. |
bEnableRamping | 1 | [TRUE,FALSE] | TRUE causes each setpoint step-change to be converted to a ramp. |
fW1 | °C | LREAL | Setpoint. |
fW2 | °C | LREAL | Standby setpoint, generally smaller than fW1. fSelSetpoint can be used to switch between fW1 and fW2. |
fX | °C | LREAL | Actual value. This value must be converted to LREAL. |
bOpenThermocouple | 1 | [TRUE,FALSE] | The thermocouple is open if TRUE. Must be indicated by the hardware (e.g. KLxxxx). |
bReverseThermocouple | 1 | [TRUE,FALSE] | TRUE indicates that the thermocouple has been connected with the wrong polarity. Must be indicated by the hardware. |
bBackVoltage | 1 | [TRUE,FALSE] | TRUE indicates that the input voltage at the thermocouple is too high. Must be indicated by the hardware. |
bLeakage | 1 | [TRUE,FALSE] | TRUE indicates that leakage current has been detected at the heating element. Must be indicated by the hardware. |
bShortCircuit | 1 | [TRUE,FALSE] | TRUE indicates that a short circuit has been detected at the heating element. Must be indicated by the hardware. |
bOpenCircuit | 1 | [TRUE,FALSE] | TRUE indicates that an open circuit has been detected at the heating element. Must be indicated by the hardware. |
sControllerParameter | none | Structure | General parameters (sampling time etc.) are passed to the function block in this structure. |
sParaControllerExternal | none | Structure | An external controller parameter set is passed to the function block in this structure. |
sLogData | none | Structure | This structure passes parameters for logging to the function block (filenames etc.). |
Outputs
fYAnalog | none | LREAL | Analog control value. |
bYPWM | none | [TRUE,FALSE] | Boolean output, pulse width modulated. |
bYDig | none | [TRUE,FALSE] | Boolean output of an on-off controller (TRUE control value 100%, FALSE control value off) |
bYDigPos | none | [TRUE,FALSE] | Boolean output of a three-step controller (TRUE control value 100%, FALSE control value off) |
bYDigNeg | none | [TRUE,FALSE] | Boolean output of a three-step controller (TRUE control value -100%, FALSE control value off) |
dwAlarm | none | DWORD | Alarm messages (see ENUM ...) |
iState | none | INT | Current controller state (see ENUM ...) |
sParaControllerInternal | none | Structure | In this structure the internal controller parameter set (determined by the tuning) is made available. |
bError | none | [TRUE,FALSE] | If an error is present, then bError is TRUE. |
iErrorId | none | INT | If bError is TRUE, then iErrorId provides an error code (see ENUM ...) |