MC_OverrideFilter
The function block MC_OverrideFilter can be used to convert an unfiltered override value consisting of digits (e.g. a voltage value of an analog input terminal) into a filtered override value that matches the cyclic axis interface (PlcToNc) (DWORD in the range 0...1000000). This filtered override is also available in percent (LREAL in the range 0...100%).
The raw input value is limited to a validity range by LowerOverrideThreshold and UpperOverrideThreshold, and implemented as parameterizable steps (resolution) (OverrideSteps). After each override change at the output of the FB, a minimum recovery time is awaited internally (OverrideRecoveryTime) before a new override value can be accepted. The only exceptions are the override values 0% and 100%, which are always implemented without delay for safety reasons.
![]() | Due to the gradation of the override output value (OverrideValueFiltered), the filtered override may become zero for very small override input values (OverrideValueRaw). A zero override leads to standstill of the axis. If total standstill is undesired, OverrideValueRaw should not fall below the smallest level. |
OverrideValueRaw : DINT;
LowerOverrideThreshold : DINT := 0; (* 0...32767 digits *)
UpperOverrideThreshold : DINT := 32767;(* 0...32767 digits *)
OverrideSteps : UDINT := 200; (* 200 steps=> 0.5 percent*)
OverrideRecoveryTime : TIME := T#150ms; (* 150 ms *)
OverrideValueRaw | Raw, unfiltered override value (e.g. a voltage value of an analog input terminal). |
LowerOverrideThreshold | The lower threshold for the raw override value. |
UpperOverrideThreshold | The upper threshold for the raw override value. |
OverrideSteps | The specified steps (override resolution). |
OverrideRecoveryTime | Minimum recovery time, after which a new filtered override value is placed on the output. The override values 0% and 100% are implemented without delay. |
Outputs
OverrideValueFiltered : DWORD; (* 0...1000000 counts *)
OverridePercentFiltered : LREAL; (* 0...100 % *)
Error : BOOL;
ErrorId : UDINT;
OverrideValueFiltered | The filtered override value in digits (the data type matches the override in the cyclic axis interface 0 to 1000000). |
OverridePercentFiltered | The filtered override value in percent (0..100%). |
Error | Becomes TRUE if an error occurs. |
ErrorID | If the error output is set, this parameter supplies the error number. |
Possible error number | Possible causes |
MC_ERROR_PARAMETER_NOT_CORRECT |