MC_OverrideFilter
Fig.2: MC_OverrideFilterThe function block MC_OverrideFilter can be used to convert an unfiltered override value consisting of digits (e.g. a voltage value of an analog input terminal) into a filtered override value that matches the cyclic axis interface (PlcToNc) (DWORD in the range 0...1000000). This filtered override is also available in percent (LREAL in the range 0...100%).
The raw input value is limited to a validity range by LowerOverrideThreshold and UpperOverrideThresholdauf, and implemented as parameterisable steps (resolution) (OverrideSteps). After each override change at the output of the FB, a minimum recovery time is awaited internally (OverrideRecoveryTime) before a new override value can be accepted. The only exceptions are the override values 0% and 100%, which are always implemented without delay for safety reasons.
OverrideValueRaw : DINT;
LowerOverrideThreshold : DINT := 0; (* 0...32767 digits *)
UpperOverrideThreshold : DINT := 32767; (* 0...32767 digits *)
OverrideSteps : UDINT := 200; (* 200 steps => 0.5 percent *)
OverrideRecoveryTime : TIME := T#150ms; (* 150 ms *)
END_VAROverrideValueRaw: Raw, unfiltered override value (e.g. a voltage value of an analog input terminal).
LowerOverrideThreshold: The lower threshold for the raw override value.
UpperOverrideThreshold: The upper threshold for the raw override value.
OverrideSteps: The specified steps (override resolution).
OverrideRecoveryTime: Minimum recovery time, after which a new filtered override value is placed on the output. The override values 0% and 100% are implemented without delay.
OverrideValueFiltered : DWORD; (* 0...1000000 counts *)
OverridePercentFiltered : LREAL; (* 0...100 % *)
Error : BOOL;
ErrorId : UDINT;
END_VAROverrideValueFiltered: The filtered override value in digits (the data type matches the override in the cyclic axis interface 0..1000000).
OverridePercentFiltered: The filtered override value in percent (0..100%).
Error: Becomes TRUE, as soon as an error occurs.
ErrorID : If the error output is set, this parameter supplies the error number.
Possible error number | Possible causes |
MC_ERROR_PARAMETER_NOT_CORRECT |
Development Enivironment | Target System | PLC Libraries to include |
TwinCAT v2.8 Build > 739 | PC (i386) | TcMC.Lib |