FB_HVACHeatingCurveEx
Application
The heating curve serves to determine the setpoint for the flow temperature of a heating circuit, depending on the outside temperature. Compared with the FB_HVACHeatingCurve, the heating curve is shown as a function.
z = 20 - rDesignTemp;
u = 20 - rOutsideTemp;
bSetDefault : BOOL;
rOutsideTempDamped : REAL;
bDayOperation : BOOL;
bReset : BOOL; eDataSecurityType:if eDataSecurityType:= eHVACDataSecurityType_Persistent, the persistent VAR_IN_OUT variables of the function block are stored in the flash of the computer if a value changes. For this to work, the function block FB_HVACPersistentDataHandling must be instanced once in the main program, which is called cyclically. Otherwise the instanced FB is not released internally.
A change of value can be initiated by the building management system, a local operating device or via a write access from TwinCAT. When the computer is restarted, the saved data are automatically read back from the flash into the RAM.
Application example:
Example_PERSISTENT.zip
Notice | |
A cyclically changing variable must never be linked with the IN_OUT variable of a function block, if eDataSecurityType:= eDataSecurityType_Persistent . It would lead to early wear of the flash memory. |
rOutsideTempDamped: this input variable transfers the current damped outside temperature to the function block.
bReset: acknowledge input in the event of a fault.
rTempSetpoint : REAL; ° C
bInvalidParameter : BOOL;rTempSetpoint: the calculated setpoint for the flow temperature.
bInvalidParameter: indicates that an incorrect input parameter is present. bInvalidParameter must be acknowledged with bReset.
rMinTempSetpoint : REAL;
rMaxTempSetpoint : REAL;
rDesignTemp : REAL;
rSlope : REAL;
rCurve : REAL; rMinTempSetpoint: the minimum value for the setpoint of the flow temperature [°C] is defined by this variable. The variable is saved persistently. Preset to 20.
rMaxTempSetpoint: the maximum value for the setpoint of the flow temperature [°C] is defined by this variable. The variable is saved persistently. Preset to 90.
rDesignTemp: design temperature [°C] for the dimensioning of a heating system. Typical values for Germany lie between -12 ° C and -16 ° C. The variable is saved persistently. Preset to -16.
rSlope: factor for the slope. The variable is saved persistently. Preset to 1.
rCurve: factor for the curve. The variable is saved persistently. Preset to 0.5.
Course of the heating characteristic curves
Flow temperature of 50 °C at approx. -9.2 °C
Flow temperature of 50 °C at approx. -9.4 °C
Flow temperature of 50 °C at approx. -7.8 °C
Flow temperature of 50 °C at approx. -8.3 °C
Flow temperature of 60 °C at approx. 0.2 °C
Flow temperature of 60 °C at approx. 3.0 °C