FB_DALIV2GetEventData
FB_DALIV2GetEventData 1:
Filters out an event specified by the event scheme.
Each event sent by a DALI device contains two fields that provide information about the event source. These two fields are a combination of the short address, instance number, instance type, instance group or device group. The recipient of the event must know which address scheme is used to send the data.
For each event that is to be received and processed further, an instance of FB_DALIV2GetEventData() must be created and configured with the correct event scheme.
bEnable            : BOOL;
eEventScheme       : E_DALIV2EventScheme := eDALIV2EventSchemeDeviceInstance;
nAddressInfo01     : BYTE;
nAddressInfo02     : BYTE;
bEnable: Enables the function block. If this input is set to FALSE, no further events are output.
eEventScheme: The event scheme defines the address information required for filtering the desired result.
nAddressInfo01: (see table below)
nAddressInfo02: (see table below)
eEventScheme
nAddressInfo01
nAddressInfo02
eDALIV2EventSchemeInstance
Instance type (0-31)
Instance number (0-31)
Short address (0-63)
eDALIV2EventSchemeDeviceGroup
Device group (0-31)
eDALIV2EventSchemeInstanceGroup
Instance group  (0-31)
bNewData      : BOOL;
nEventInfo    : WORD;
bNewData: If an event was received that corresponds to the event scheme and address information, this output is set to TRUE for one PLC cycle.
nEventInfo: If the output bNewData is TRUE, further information about the event can be found at this output. The exact meaning depends on the device type and is described in the respective Part 3xx of IEC 62386.
stCommandBuffer   : ST_DALIV2CommandBuffer;
stCommandBuffer: Reference to the internal structure for communication with the function block FB_KL6821Communication() (KL6821).
Development environment
Target system
Required libraries
TwinCAT 2.11 R3/x64 from build 2260
PC/CX, BX or BC
TcDALIV2 library from V2.12.0
