FB_CTRL_ARITHMETIC_MEAN
Calculating the mean value:
fIn : FLOAT;
fManSyncValue : FLOAT;
bSync : BOOL;
eMode : E_CTRL_MODE;
bHold : BOOL;
fIn : Input value for the mean value filter.
fManSyncValue : Input value to which the mean value filter can be set, or that is issued at the output in manual mode.
bSync : A rising edge at this input sets the mean value filter to the value fManSyncValue.
eMode : Input that specifies the block's operating mode.
bHold : A TRUE at this input will hold the internal state (and therefore also the output) constant at its current value, independently of the input value.
fOut : FLOAT;
eState : E_CTRL_STATE;
eErrorId : E_CTRL_ERRORCODES;
fOut : Output of the mean value filter.
eState : State of the function block.
eErrorId : Supplies the error number when the bError output is set.
bError : Becomes TRUE, as soon as an error occurs.
stParams : ST_CTRL_ARITHMETIC_MEAN_PARAMS;
stParams : Parameter structure of the average filter. This consists of the following elements:
TYPE
ST_CTRL_ARITHMETIC_MEAN_PARAMS:
STRUCT
tCtrlCycleTime : TIME := T#0ms; (* controller
cycle time [TIME] *)
tTaskCycleTime : TIME := T#0ms; (* task cycle
time [TIME] *)
END_STRUCT
END_TYPE
tCtrlCycleTime : Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycleTime : Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.