FB_CTRL_I
FB_CTRL_I 1:
The function block provides an I-transfer element in the functional diagram.
Transfer function:
FB_CTRL_I 2:
    fIn         : FLOAT;
    fManSyncValue   : FLOAT;
    bSync       : BOOL;
    eMode       : E_CTRL_MODE;
    bHold       : BOOL;
fIn : Input of the I element.
fManSyncValue : Input to which the I-element can be synchronised, or whose value is the present at the output in Manual Mode.
bSync : A rising edge at this input sets the integrator to the value fManSyncValue.
eMode : Input that specifies the block's operating mode.
bHold : A TRUE at this input holds the integrator fixed at the current value, independently of the input fIn.
    fOut        : FLOAT;
    bARWactive      : BOOL;
    eState      : E_CTRL_STATE;
    eErrorId        : E_CTRL_ERRORCODES;
    bError      : BOOL;
fOut : Output of the I element.
bARWactive : A TRUE at this output signals that the integrator is being restricted.
eState : State of the function block.
nErrorID : Returns the ADS error number when the bError output is set.
bError: Becomes TRUE, as soon as an error occurs.
    stParams        : ST_CTRL_I_PARAMS;
stParams : Parameter structure of the I element. This consists of the following elements:
TYPE ST_CTRL_I_PARAMS
STRUCT
    tCtrlCycleTime : TIME  :=  T#0ms; (* controller cycle time
    tTaskCycleTime : TIME  :=  T#0ms; (* task cycle time
    tTi        : TIME  :=  T#0ms; (* integral action time
Ti *)
    fOutMaxLimit   : FLOAT :=  1E38;  (* maximum output limit
    fOutMinLimit   : FLOAT := -1E38;  (* minimum output limit
END_STRUCT
END_TYPE
tCtrlCycleTime : Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycleTime : Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
tTi : Integration time of the I element.
fOutMaxLimit : Upper limit at which integration is halted (ARW measure). Reaching this limit is indicated by a TRUE at the bARWActive output.
fOutMinLimit : Lower limit at which integration is halted (ARW measure). Reaching this limit is indicated by a TRUE at the bARWActive output.
Development Environment
Target System
PLC libraries to include
TwinCAT v2.8
PC (i386)
TcControllerToolbox.lib
TwinCAT v2.9 from Build 947
BC
TcControllerToolbox.lb6
TwinCAT v2.9 from Build 956
BX
TcControllerToolbox.lbx