FB_CTRL_HYSTERESIS
FB_CTRL_HYSTERESIS 1:
The function block provides a hysteresis transfer element in a functional diagram.
Transfer function:
FB_CTRL_HYSTERESIS 2:
    fIn            : FLOAT;
    bManSyncValue  : BOOL;
    bSync          : BOOL;
    eMode          : E_CTRL_MODE;
fIn : Input of the hysteresis element.
bManSyncValue : Input through which the hysteresis element can be set to one of the two junctions.
bSync : A rising edge at this input sets the hysteresis element to the value fManSyncValue.
eMode : Input that specifies the operation mode of the function block.
    bOut        : BOOL;
    eState      : E_CTRL_STATE;
    eErrorId        : E_CTRL_ERRORCODES;
    bError      : BOOL;
bOut : Output of the hysteresis element.
eState : State of the function block.
eErrorId : Supplies the error number when the bError output is set.
bError : Becomes TRUE as soon as an error situation occurs.
    stParams        : ST_CTRL_HYSTERESIS_PARAMS;
stParams : Parameter structure of the hysteresis element. This consists of the following elements:
TYPE
ST_CTRL_HYSTERESIS_PARAMS :
STRUCT
    tCtrlCycleTime     : TIME := T#0ms; (* controller cycle
time [TIME] *)
    tTaskCycleTime     : TIME := T#0ms; (* task cycle time
[TIME] *)
    fHysteresisRange   : FLOAT; (* range of the hysteresis loop
END_STRUCT
END_TYPE
tCtrlCycleTime : Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycleTime : Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
fHysteresisRange : Hysteresis range, see image above.
Development Environment
Target System
PLC libraries to include
TwinCAT v2.8
PC (i386)
TcControllerToolbox.lib
TwinCAT v2.9 ab Build 947
BC
TcControllerToolbox.lb6
TwinCAT v2.9 ab Build 956
BX
TcControllerToolbox.lbx