FB_CTRL_D
FB_CTRL_D 1:
The function block provides a DT1 transfer element (a real D element) in a functional diagram.
Transfer function (continuous):
FB_CTRL_D 2:
    fIn            : FLOAT;
    fManSyncValue  : FLOAT;
    bSync          : BOOL;
    eMode          : E_CTRL_MODE;
fIn : Input of the D element.
fManSyncValue : Input to which the D element can be synchronized, or whose value is present at the output in Manual Mode.
bSync : A rising edge at this input sets the D element to the value fManSyncValue.
eMode : Input that specifies the operation mode of the function block.
    fOut        : FLOAT;
    eState      : E_CTRL_STATE;
    eErrorId    : E_CTRL_ERRORCODES;
    bError      : BOOL;
fOut : Output of the D element.
eState : State of the function block.
nErrorID : Returns the ADS error number when the bError output is set.
bError: Becomes TRUE, as soon as an error occurs.
    stParams        : ST_CTRL_D_PARAMS;
stParams : Parameter structure of the D element. This consists of the following elements:
TYPE ST_CTRL_D_PARAMS
STRUCT
    tCtrlCycleTime     : TIME     :=  T#0ms; (* controller
cycle time [TIME] *)
    tTaskCycleTime     : TIME     :=  T#0ms; (* task cycle time
[TIME] *)
    tTv        : TIME     :=  T#0ms; (* derivative
action time Tv *)
    tTd        : TIME     :=  T#0ms; (* derivative
damping time Td *)
    fOutMaxLimit       : FLOAT    :=  1E38;  (* maximum output
limit *)
    fOutMinLimit       : FLOAT    := -1E38;  (* minimum output
limit *)
END_STRUCT
END_TYPE
tCtrlCycleTime : Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycleTime : Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
tTv : Differentiation time constant
tTd : Damping time constant
fOutMaxLimit : Upper limit at which the output of the D element is limited.
fOutMinLimit : Lower limit at which the output of the D element is limited.
Development Environment
Target System
PLC libraries to include
TwinCAT v2.8
PC (i386)
TcControllerToolbox.lib
TwinCAT v2.9 from Build 947
BC
TcControllerToolbox.lb6
TwinCAT v2.9 from Build 956
BX
TcControllerToolbox.lbx