WritePersistentData
If persistent variables are defined in a PLC runtime system, their current values are normally saved in a .bootdata file in the TwinCAT\Boot folder when stopping/shutting down the TwinCAT system (following the last PLC cycle). Before writing the current persistent data to the file, a backup of the old persistent data is made by renaming the system's old .bootdata file to .bootdata-old.
A file is created for every runtime system that is configured.
The next time the system starts, the .bootdata file is read and the persistent variables in the runtime system are initialized with the values from the file.
This backup file (.bootdata-old) of the persistent data is read at system startup if the file (.bootdata) containing the persistent data does not exist. This is an exception, but it can occur, for example, if an IPC without UPS experiences a power failure and TwinCAT could not shut down properly.
With the function block WritePersistentData you can initiate the saving of the persistent data from the PLC program and ensure that an up-to-date .bootdata file with the persistent data is available. The PORT input parameter specifies the runtime system whose persistent data is to be saved.
    NETID  : T_AmsNetId;
    PORT   : T_AmsPort;
    START  : BOOL;
    TMOUT  : TIME := DEFAULT_ADS_TIMEOUT;
END_VAR| Name | Type | Description |
| NETID | T_AmsNetID | Network address of the TwinCAT computer on which the ADS command is to be executed. An empty string can be entered for the local computer |
| PORT | T_AmsPort | ADS port number of the PLC runtime system whose persistent data is to be saved. |
| START | BOOL | The function block is enabled by a positive edge at this input. |
| TMOUT | TIME | Time-out period that may not be exceeded when executing the ADS command. |
 Outputs
 Outputs
    BUSY   : BOOL;
    ERR    : BOOL;
    ERRID  : UDINT;
| BUSY | BOOL | When the function block is enabled, this output is set and remains set until a feedback is received. |
| ERR | BOOL | If an ADS error should occur during the transfer of the command, then this output is set once the BUSY output is reset. |
| ERRID | UDINT | Returns the ADS error number when the ERR output is set. |
Example:
PROGRAM MAIN
    bStart                : BOOL;
    bError                : BOOL;
    bBusy                 : BOOL;
    nErrorId              : UDINT;
    fbWritePersistentData : WritePersistentData;
    fbR_Trig              : R_TRIG;
END_VARVAR PERSISTENT
    perA  : INT;
    perB  : BOOL;
    perC  : BYTE;
    perD  : STRING;
    perE  : ARRAY[0..10] OF INT;
    perF  : ARRAY[0..10] OF UDINT;
END_VARfbR_Trig( CLK:=bStart );
IF fbR_Trig.Q THEN
    perA := 24443;
    perB := TRUE;
    perC := 7;
    perD := 'Switch ON/OFF';
    perE[ 0 ] := 1;
    perE[ 10 ] := 11;
    perF[ 0 ] := 263;
    perF[ 10 ] := 23323;
    fbWritePersistentData(NETID:='', PORT:=851, START:=bStart, TMOUT:=T#1s );
ELSE
    fbWritePersistentData( START:=FALSE);
END_IF;
bBusy := fbWritePersistentData.BUSY;
bError := fbWritePersistentData.ERR;
nErrorId := fbWritePersistentData.ERRID;See also: Appendix > System behavior when writing persistent data
| Development environment | Target platform | PLC libraries to be integrated (category group) |
| TwinCAT v3.1.0 | PC or CX (x86, x64, Arm®) | Tc2_Utilities (System) |
