FB_CXSimpleUps
The function block FB_CXSimpleUps can be used on the CX1000 or CX1020 in order to activate the UPS CX1190-UPS from the PLC. In this case the UPS settings must be deactivated in the TwinCAT System Manager.
bDIPDisable : BOOL;
iDischargeLevel : USINT;
tDelay : TIME;
bDIPDisable | BOOL | If bDIPDIsable = TRUE, then the position of the charge level switch on the UPS is ignored and iDischargeLevel is used instead. |
iDischargeLevel | USINT | Discharge switch-off threshold: 0 = 100% (maximum discharge), 9 = 90%, 8 = 80%, ..., 2 = 20%, 1 = 10% (minimum discharge). |
tDelay | TIME | Holding time before the shutdown is carried out. It is used to bridge short power failures (up to 10 s). |
Outputs
bPowerFailure : BOOL;
bShutdownActive : BOOL;
bUpsReady : BOOL;
b24VInOK : BOOL;
bHolding : BOOL;
tTimeUntilShutdown : TIME;
eUpsState : E_UPS_STATE;
bPowerFailure | BOOL | Becomes TRUE when a power failure of the supply voltage is detected, becomes FALSE when the input voltage returns. |
bShutdownActive | BOOL | Becomes TRUE as soon as the stop or shutdown is executed. |
bUpsReady | BOOL | Becomes TRUE as soon as the 24 V input voltage is available. |
b24VInOK | BOOL | Becomes TRUE as soon as the UPS provides the output voltage. |
bHolding | BOOL | Becomes TRUE as soon as a failure in the supply voltage has been detected, and the holding time has not yet elapsed. |
tTimeUntilShutdown | TIME | Indicates the holding time remaining until shutdown. |
eUpsState | E_UPS_STATE | Displays the status of the UPS [UNDEF | CHARGING | CHARGED | DISCHARGE | DISCHARGE_RESTART | OUTPUT_OFF | OVERLOAD]. |
Configuration variables
VAR_CONFIG
Ii24VState AT %I* : BYTE;
IiChargeState AT %I* : USINT;
QiControl AT %Q* : BYTE;
QiDipControl AT %Q* : USINT;
Ii24VState | BYTE | Must be linked with input '24V State', see picture above. |
IiChargeState | USINT | Must be linked with input 'Charge State', see picture above. |
QiControl | BYTE | Must be linked with output 'Contol', see picture above. |
QiDipControl | USINT | Must be linked with output 'DIP Ctrl', see picture above. |
TwinCAT v3.1.0 | CX (x86) | Tc2_SystemCX |
![]() | For other CX and PC refer to the function block FB_S_SUPS_BAPI in the Tc2_SUPS library. |