ADSWRTCTL
ADSWRTCTL 1:
This function block permits the execution of an ADS control command to affect the state of an ADS device, e.g. to start, stop or reset a device.
ADSWRTCTL 2: Inputs
    NETID     : T_AmsNetId;
    PORT      : T_AmsPort;
    ADSSTATE  : UINT;
    DEVSTATE  : UINT;
    LEN       : UDINT;
    SRCADDR   : PVOID;
    WRITE     : BOOL;
    TMOUT     : TIME := DEFAULT_ADS_TIMEOUT;
Type
NETID
T_AmsNetId
String containing the AMS network ID of the target device to which the ADS command is addressed (type: T_AmsNetId).
PORT
T_AmsPort
Port number of the ADS device (type: T_AmsPort).
ADSSTATE
UINT
State identification code of the ADS target device.
DEVSTATE
UINT
Contains the specific state identification code of the ADS target device. The codes given here are supplementary information which is specific to the ADS device.
LEN
UDINT
Number of data to be written in bytes.
SRCADDR
PVOID
Address of the buffer from which the data to be written is to be fetched. The programmer is himself responsible for dimensioning the buffer to such a size that 'LEN' bytes can be taken from it. The buffer can be a single variable, an array or a structure, whose address can be found with the ADR operator.
WRITE
The ADS command is triggered by a rising edge at this input.
TMOUT
TIME
Indicates the time before the function is canceled.
The codes shown here are specified for all ADS servers:
ADSWRTCTL 3: Outputs
    BUSY    : BOOL;
    ERR     : BOOL;
    ERRID   : UDINT;
Type
BUSY
This output remains TRUE until the function block has executed a command, but at the longest for the duration supplied to the Timeout input. No new commands are accepted at the inputs as long as BUSY = TRUE. Note that it is not the execution of the service but its acceptance whose time is monitored.
ERR
This output is switched to TRUE as soon as an error occurs during the execution of a command. The command-specific error code is contained in ERRID. If the function block has a timeout error, ERR is TRUE and ERRID is 1861 (hexadecimal 0x745). Is reset to FALSE by the execution of a command at the inputs.
ERRID
UDINT
ADS error code or command-specific error code of the last executed command. Is reset to 0 by the execution of a command at the inputs.
Example of calling the block in FBD:
ADSWRTCTL 4:
In the example a reset command (ADSSTATE=2) is sent to the I/O server (Port300), along with supplementary data hex.AFFE. As a result the I/O server executes a bus reset.
Development environment
Target system type
PLC libraries to include (Category group)
TwinCAT v3.1.0
PC or CX (x86, x64, ARM)
Tc2_System (System)