FB_SoEReadClassXDiag
With the function block FB_SoEReadClassXDiag, the current Class 1 diagnosis (S-0-0011) ... Class 3 diagnosis (S-0-0013) can be read out as WORD. There is the conversion function F_ConvWordToSTAX5000C1D for the evaluation of the Class 1 diagnosis as a structure ST_AX5000_C1D, (see TwinCAT 3 PLC Lib Tc2_Drive documentation).
NetId : T_AmsNetId := '';
Execute : BOOL;
DiagClass : USINT:= 1; (* 1: C1D (S-0-0011) is default, 2: C2D (S-0-0012), 3: C3D (S-0-0013) *)
Timeout : TIME := DEFAULT_ADS_TIMEOUT;
NetId | T_AmsNetId | String, which contains the AMS Network ID of the PC (type: T_AmsNetId). |
Execute | BOOL | The function block is enabled via a positive edge at this input. |
DiagClass | USINT | Specifies which diagnosis should be read. The diagnostics parameters may vary from vendor to vendor. All diagnostics parameters (C1D ... C3D) or all bits are not always implemented in them. 1: Error: Class 1 Diag (S-0-0011) 2: Warnings: Class 2 Diag (S-0-0012) 3: Information: Class 3 Diag (S-0-0013) |
Timeout | TIME | Maximum time allowed for the execution of the function block. |
Inputs/outputs
Axis : AXIS_REF;
Axis | Axis data structure that unambiguously addresses an axis in the system. Among other parameters it contains the current axis status, including position, velocity or error state. |
Outputs
Busy : BOOL;
Error : BOOL;
AdsErrId : UINT;
SercosErrId : UINT;
ClassXDiag : WORD;
Attribute : DWORD;
Busy | BOOL | This output is set when the function block is activated, and remains set until a feedback is received. |
Error | BOOL | This output is set after the Busy output has been reset when an error occurs in the transmission of the command. |
AdsErrId | UINT | In the case of a set Error output returns the ADS error code of the last executed command. |
SercosErrId | UINT | In the case of a set Error output returns the Sercos error of the last executed command. |
ClassXDiag | WORD | Returns the current Class X diagnosis. |
Attributes | DWORD | Returns the attributes of the Sercos parameter. |
Sample
fbClassXDiag : FB_SoEReadClassXDiag;
bClassXDiag : BOOL;
DiagClass : USINT := 1;
Class1Diag : WORD;
stAX5000C1D : ST_AX5000_C1D;
Class2Diag : WORD;
(* NcAxis *)
Axis : AXIS_REF;
IF bClassXDiag THEN
fbClassXDiag(
Axis := Axis,
Execute := TRUE,
DiagClass := DiagClass,
Timeout := DEFAULT_ADS_TIMEOUT
IF NOT fbClassXDiag.Busy THEN
fbClassXDiag(Axis := Axis, Execute := FALSE);
bClassXDiag := FALSE;
CASE fbClassXDiag.DiagClass OF
1:
Class1Diag := fbClassXDiag.ClassXDiag;
stAX5000C1D := F_ConvWordToSTAX5000C1D(Class1Diag);
2:
Class2Diag := fbClassXDiag.ClassXDiag;
END_CASE
END_IF
END_IF