MC_ReadStopInfo
MC_ReadStopInfo 1:
The MC_ReadStopInfo function block can be used to calculate the distance and time to a complete stop of the axis, based on the specified dynamics.
It should be noted that while the calculated values provide an estimate, the actual distance and time to a standstill may differ from these values due to ADS runtimes, depending on the prevailing dynamics.
MC_ReadStopInfo 2: Inputs
    Execute           : BOOL;
    Deceleration      : LREAL;
    Jerk              : LREAL;
Type
Execute
The command is executed with a rising edge.
Deceleration
LREAL
Deceleration (≥0)
If the value is 0, the default deceleration from the axis configuration is applied.
Jerk
LREAL
Jerk (≥0)
If the value is 0, the default jerk from the axis configuration is applied.
MC_ReadStopInfo 3: Inputs/outputs
    Axis : AXIS_REF;
Type
Axis
AXIS_REF
Axis data structure that unambiguously addresses an axis in the system. Among other parameters it contains the current axis status, including position, velocity or error state.
MC_ReadStopInfo 4: Outputs
    BitValues         : DWORD;
    Done              : BOOL;
    Busy              : BOOL;
    Error             : BOOL;
    ErrorID           : UDINT;
Type
BitValues
DWORD
Values of the corresponding read bits.
Done
TRUE if the command was executed without errors.
Busy
TRUE as soon as the command is started with Execute and as long as the command is processed. If "Busy" is FALSE, the function block is ready for a new order.
Error
TRUE, if an error occurs.
ErrorID
UDINT
If the error output is set, this parameter supplies the error number.
StopDistance
LREAL
Distance until the axle comes to a stop
StopTime
LREAL
Time to axle stop [s]
Development environment
Target platform
PLC library to include
TwinCAT v3.1.4024.79
TwinCAT v3.1.4026
TF5000.NCPTP.XAE 1.0.11
PC oder CX (x86)
Tc2_MC2 v3.3.75