FB_EcSetSlaveState
FB_EcSetSlaveState 1:
With this function block a slave can be set to a specified EtherCAT state. The requested EtherCAT state is transferred with the reqState variable. The function block sends the command to change state and, unlike the function block FB_EcRegSlaveState, remains active until the EtherCAT slave has attained the new state or the maximum time tTimeout is exceeded. The current state is output in the currState variable.
See also: FB_EcReqSlaveState
FB_EcSetSlaveState 2: Inputs
    sNetId     : T_AmsNetId;
    nSlaveAddr : UINT;
    bExecute   : BOOL;
    tTimeout   : TIME := T#10s;
    reqState   : WORD;
Type
sNetId
T_AmsNetId
String containing the AMS network ID of the EtherCAT master device. (Type: T_AmsNetId)
nSlaveAddr
UINT
Fixed address of the EtherCAT slave whose EtherCAT state is to be set.
bExecute
The function block is activated by a positive edge at this input.
tTimeout
TIME
Maximum time allowed for the execution of the function block.
reqState
WORD
EtherCAT state to which the slave is to be set. (See reqState)
reqState
EtherCAT state to which the slave is to be set. The possible values for reqState are:
Constant
Value
EC_DEVICE_STATE_INIT
0x01
Set slave to Init state
EC_DEVICE_STATE_PREOP
0x02
Set slave to Pre-operational state
EC_DEVICE_STATE_BOOTSTRAP
0x03
Set slave to Bootstrap state. This state is used for firmware downloads.
EC_DEVICE_STATE_SAFEOP
0x04
Set slave to Safe-operational state
EC_DEVICE_STATE_OP
0x08
Set slave to Operational state
EC_DEVICE_STATE_ERROR
0x10
If the error bit in the status byte is set in the EtherCAT slave (currState.deviceState AND EC_DEVICE_STATE_ERROR = TRUE), the error bit can be reset by setting EC_DEVICE_STATE_ERROR.
FB_EcSetSlaveState 3: Outputs
    bBusy     : BOOL;
    bError    : BOOL;
    nErrId    : UDINT;
    currState : ST_EcSlaveState;
Type
bBusy
This output is set when the function block is activated, and remains set until a feedback is received.
This output is set after the bBusy output has been reset when an error occurs in the transmission of the command.
nErrId
UDINT
Supplies the ADS error code associated with the most recently executed command if the bError output is set.
currState
ST_EcSlave
State
Current EtherCAT state of the slave
Development environment
Target platform
PLC libraries to include
TwinCAT v3.1.0
PC or CX (x86, x64, ARM)
Tc2_EtherCAT