Error codes
Value (hex)
Value (dec)
Value (enum)
0x0000
0
NO_EIB_ERROR
No error.
0x0001
1
WRONG_EIB_PHYS_ADDR
Outdated, no longer used.
0x0002
2
WRONG_EIB_GROUP_ADDR
The input variable EIB_GROUP_FILTER.GROUP_ADDR is faulty. Check GROUP_ADDR of your filters. MAIN must be less than 16, SUB_MAIN less than 8.
0x0003
3
WRONG_EIB_GROUP_LEN
The input variable EIB_GROUP_FILTER.GROUP_LEN is faulty. Incorrect filter length. Check the mode and the length of the filters.
0x0004
4
WRONG_EIB_NO_FILTER
No filter detected. Check your filter in EIB_GROUP_FILTER and the mode.
0x0005
5
WRONG_EIB_IDX_RANGE
The input variable idx has an incorrect value.
0x000A
10
WRONG_EIB_FIRMWARE
The mode is not supported with this firmware.
0x000B
11
WRONG_EIB_MODE
Unsupported mode during parameterization. Check iMode. Permitted values are 0, 1 and 100.
0x000C
12
WRONG_MODE
The input variable iMode has an incorrect value.
0x000E
14
WRONG_EIB_FIRMWARE_B1_NECESSARY
Firmware B1 or higher required.
0x000F
15
WRONG_EIB_FIRMWARE_B3_NECESSARY
Firmware B3 or higher required.
0x0014
20
WRONG_EIB_DATA_LEN
Expected data length of the EIB telegram is wrong. Telegram is discarded. Check the EIB group addresses and/or the data type used.
0x0015
21
ERROR_EIB_SERVICE_NOT_SUPPORT
A EIB telegram is not supported.
0x001E
30
KL6301_TP_TOGGLE_ERROR
Terminal did not respond for one second. Check the connection with the KL6301. Is it still busy with data exchange?
0x001F
31
TIME_OUT
The terminal fails to respond during parameterization. Check the connection with the KL6301.
0x0020
32
KL6301_NO_RESPONSE_FROM_TERMINAL
No connection to KL6301. Either terminal not available or mapping incorrect.
0x0028
40
ERROR_SEND_8BIT_WRONG_Scaling_Mode
Incorrect or unsupported Scaling mode.
0x0064
100
ERROR_EIB_PHY_ADDR_NOT_SUPPORT
Physical addressing not permitted.
0x0065
101
ERROR_EIB_WRITE_DATA
Outdated. No longer used.
0x0066
102
MONITOR_MODE_LEN_IS_NOT_OK_MUST_0
For Monitor mode the filter length must be 0.
0x0067
103
MONITOR_MODE_ADDR_IS_NOT_OK_MUST_0
For Monitor mode the addresses must be 0.
0x0068
104
WATCHDOG_ERROR_NO_SEND
Data transfer not possible. The group address for which the data transfer has failed can be found in the local variable "NotSendGroup" of function block KL6301.
0x0BBB
3003
ERROR_EIB_NO_ACK
No ACK received.
0xFAFB
64251
ERROR_EIB_NO_COM_TO_TP
No communication with the EIB hardware.
0x0FCC
4044
ERROR_TP_TEMP_WARNING
Temperature in KL6301 exceeded.
0x17CC
6092
ERROR_TP_PROTOCOL_ERROR
Protocol error in EIB hardware.
0x27CC
10188
ERROR_TP_TRANSMITTER_ERROR
0x47CC
18380
ERROR_TP_RECEIVE_ERROR
0x87CC
34764
ERROR_TP_SLAVE_COLLISION
Too many collisions in the EIB hardware. Reduce the EIB load.