FB_SoEReadClassXDiag_ByDriveRef
With the FB_SoEReadClassXDiag_ByDriveRef function block the current class 1 diagnosis (S-0-0011) ... class 3 diagnosis (S-0-0013) can be read as WORD. For the evaluation of the class 1 diagnosis as structure ST_AX5000_C1D there is a conversion function F_ConvWordToSTAX5000C1D.
stDriveRef : ST_DriveRef;
bExecute : BOOL;
iDiagClass : USINT:= 1; (* 1: C1D (S-0-0011) is default, 2: C2D (S-0-0012), 3: C3D (S-0-0013) *)
stDriveRef | ST_DriveRef | Reference to the drive. The reference to the drive can be linked directly to the PLC in the System Manager. To do this, an instance of the structure ST_PlcDriveRef must be allocated and the NetID must be converted from the byte array into a string (Type: ST_DriveRef). |
bExecute | BOOL | The function block is activated by a positive edge at this input. |
iDiagClass | USINT | Specifies which diagnosis should be read. The diagnostic parameters may vary from vendor to vendor. Not all diagnostic parameters (C1D ... C3D) or bits within them are implemented. 1: Error: Class 1 Diag (S-0-0011) 2: Warnings: Class 2 Diag (S-0-0012) 3: Information: Class 3 Diag (S-0-0013) |
tTimeout | TIME | Maximum time allowed for the execution of the function block. |
Outputs
iAdsErrId : UINT;
iSercosErrId : UINT;
dwAttribute : DWORD;
wClassXDiag : WORD;
bBusy | BOOL | This output is set when the function block is activated, and remains set until feedback is received. |
bError | BOOL | This output is set after the bBusy output has been reset when an error occurs in the transmission of the command. |
iAdsErrId | UINT | Returns the ADS error code of the last executed command when the bError output is set. |
iSercosErrId | UINT | Returns the Sercos error of the last executed command in the event of a set bError output. |
dwAttribute | DWORD | Returns the attributes of the Sercos parameter. |
wClassXDiag | WORD | Returns the current Class X diagnosis. |
Sample
fbClassXDiag : FB_SoEReadClassXDiag_ByDriveRef;
bClassXDiag : BOOL;
iDiagClass : USINT := 1;
wClass1Diag : WORD;
stAX5000C1D : ST_AX5000_C1D;
wClass2Diag : WORD;
bInit : BOOL := TRUE;
stPlcDriveRef AT %I* : ST_PlcDriveRef;
IF bInit THEN
stDriveRef.sNetId := F_CreateAmsNetId(stPlcDriveRef.aNetId);
stDriveRef.nSlaveAddr := stPlcDriveRef.nSlaveAddr;
stDriveRef.nDriveNo := stPlcDriveRef.nDriveNo;
stDriveRef.nDriveType := stPlcDriveRef.nDriveType;
IF (stDriveRef.sNetId <> '') AND (stDriveRef.nSlaveAddr <> 0) THEN
bInit := FALSE;
END_IF
END_IF
IF bClassXDiag AND NOT bInit THEN
fbClassXDiag(
stDriveRef := stDriveRef,
bExecute := TRUE,
iDiagClass := iDiagClass,
tTimeout := DEFAULT_ADS_TIMEOUT
IF NOT fbClassXDiag.bBusy THEN
fbClassXDiag(stDriveRef := stDriveRef, bExecute := FALSE);
bClassXDiag := FALSE;
CASE fbClassXDiag.iDiagClass OF
1:
wClass1Diag := fbClassXDiag.wClassXDiag;
stAX5000C1D := F_ConvWordToSTAX5000C1D(wClass1Diag);
2:
wClass2Diag := fbClassXDiag.wClassXDiag;
END_CASE
END_IF
END_IF