FB_SoEWriteCommandControl_ByDriveRef
FB_SoEWriteCommandControl_ByDriveRef 1:
With the FB_SoEWriteCommandControl_ByDriveRef function block a command can either be prepared, started or aborted.
FB_SoEWriteCommandControl_ByDriveRef 2: Inputs
    stDriveRef : ST_DriveRef;
    nIdn       : WORD;
    eCmdControl: E_SoE_CmdControl;
    bExecute   : BOOL;
    tTimeout   : TIME := DEFAULT_ADS_TIMEOUT;
Type
stDriveRef
ST_DriveRef
Reference to the drive. The reference to the drive can be linked directly to the PLC in the System Manager. To do this, an instance of the structure ST_PlcDriveRef must be allocated and the NetID must be converted from the byte array into a string (Type: ST_DriveRef).
eCmdControl
E_SoE_CmdControl
Indicates, if a command should be prepared (eSoE_CmdControl_Set := 1), executed (eSoE_CmdControl_SetAndEnable := 3) or aborted (eSoE_CmdControl_Cancel := 0).
bExecute
The command is executed with a rising edge at the Execute input.
tTimeout
TIME
Maximum time (10 s) allowed for the execution of the function block.
FB_SoEWriteCommandControl_ByDriveRef 3: Outputs
    bBusy        : BOOL;
    bError       : BOOL;
    iAdsErrId    : UINT;
    iSercosErrId : UINT;
Type
bBusy
This output is set when the function block is activated, and remains set until feedback is received.
This output is set after the bBusy output has been reset when an error occurs in the transmission of the command.
iAdsErrId
UINT
Returns the ADS error code of the last executed command when the bError output is set.
iSercosErrId
UINT
Returns the Sercos error of the last executed command in the event of a set bError output.
Sample
fbWriteCommandControl : FB_SoEWriteCommandControl_ByDriveRef;
bWriteCommandControl  : BOOL;
nIdn                  : WORD;
eCmdControl           : E_SoE_CmdControl;
stPlcDriveRef AT %I* : ST_PlcDriveRef;
IF bInit THEN
    stDriveRef.sNetId     := F_CreateAmsNetId(stPlcDriveRef.aNetId);
    stDriveRef.nSlaveAddr := stPlcDriveRef.nSlaveAddr;
    stDriveRef.nDriveNo   := stPlcDriveRef.nDriveNo;
    stDriveRef.nDriveType := stPlcDriveRef.nDriveType;
    IF (stDriveRef.sNetId <> '') AND (stDriveRef.nSlaveAddr <> 0) THEN
        bInit := FALSE;
    END_IF
END_IF
IF bWriteCommandControl AND NOT bInit THEN
    nIdn := P_0_IDN + 160;
    fbWriteCommandControl(
        stDriveRef := stDriveRef,
        bExecute := TRUE,
        tTimeout := DEFAULT_ADS_TIMEOUT,
        nIdn := nIdn,
        eCmdControl := eCmdControl
    IF NOT fbWriteCommandControl.bBusy THEN
        fbWriteCommandControl(stDriveRef := stDriveRef, bExecute := FALSE);
        bWriteCommandControl := FALSE;
    END_IF
END_IF