FB_SoEReset_ByDriveRef
FB_SoEReset_ByDriveRef 1:
The drive (S-0-0099) can be reset with the function block FB_SoEReset_ByDriveRef. In the case of multiple-channel devices if necessary, both channels will have to perform a reset. The timeout time must be 10 s, as the reset can take up to 10 s depending on the error. An NC reset will not be performed.
FB_SoEReset_ByDriveRef 2: Inputs
    stDriveRef : ST_DriveRef;
    bExecute   : BOOL;
    tTimeout   : TIME := T#10s;
Type
stDriveRef
ST_DriveRef
Reference to the drive. The reference to the drive can be linked directly to the PLC in the System Manager. To do this, an instance of the structure ST_PlcDriveRef must be allocated and the NetID must be converted from the byte array into a string (Type: ST_DriveRef).
bExecute
The command is executed with a rising edge at the Execute input.
tTimeout
TIME
Maximum time (10 s) allowed for the execution of the function block.
FB_SoEReset_ByDriveRef 3: Outputs
    bBusy        : BOOL;
    bError       : BOOL;
    iAdsErrId    : UINT;
    iSercosErrId : UINT;
Type
bBusy
This output is set when the function block is activated, and remains set until feedback is received.
This output is set after the bBusy output has been reset when an error occurs in the transmission of the command.
iAdsErrId
UINT
Returns the ADS error code of the last executed command when the bError output is set.
iSercosErrId
UINT
Returns the Sercos error of the last executed command in the event of a set bError output.
Sample
fbSoEReset : FB_SoEReset_ByDriveRef;
bSoEReset : BOOL;
stPlcDriveRef AT %I* : ST_PlcDriveRef;
IF bInit THEN
   stDriveRef.sNetId  := F_CreateAmsNetId(stPlcDriveRef.aNetId);
   stDriveRef.nSlaveAddr := stPlcDriveRef.nSlaveAddr;
   stDriveRef.nDriveNo := stPlcDriveRef.nDriveNo;
   stDriveRef.nDriveType := stPlcDriveRef.nDriveType;
   IF (stDriveRef.sNetId <> '') AND (stDriveRef.nSlaveAddr <> 0) THEN
     bInit := FALSE;
   END_IF
END_IF
IF bSoEReset AND NOT bInit THEN
  fbSoEReset(
    stDriveRef := stDriveRef,
    bExecute := TRUE,
    tTimeout := DEFAULT_ADS_TIMEOUT
  IF NOT fbSoEReset.bBusy THEN
    fbSoEReset(stDriveRef := stDriveRef, bExecute := FALSE);
    bSoEReset := FALSE;
   END_IF