CouplerReset
The CouplerReset function block can be used to execute a reset of the coupler via the 2-byte PLC interface. In a coupler reset the current terminal configuration, for example, is read in again by the coupler via the K-bus (the terminal bus), and communication on the K-bus is reinitialized. Existing K-bus error messages for the coupler are reset. The STATE and CONTROL variables are used to perform a handshake with the coupler while the function block is being executed. These variables must therefore be linked with the status/control I/O variables of the 2-byte PLC interface in the TwinCAT System Manager.
STATE : PLCINTFSTRUCT;
START : BOOL;
TMOUT : TIME;
STATE: Status word of the 2-byte PLC interface. (PLCINTFSTRUCT)
START: The function block is activated by a positive edge at this input.
TMOUT: States the length of the timeout that may not be exceeded during execution of the function.
CONTROL : PLCINTFSTRUCT;
BUSY : BOOL;
ERR : BOOL;
ERRID : UDINT;
CONTROL: Control word of the 2-byte PLC interface (PLCINTFSTRUCT).
BUSY: This output is set when the block is activated, and remains set until execution of the function has been completed.
ERR: If an error should occur during the execution of the function, then this output is set, after the BUSY output has been reset.
ERRID: Supplies the error number when the ERR output is set.
Error number | Error description |
0 | no error |
0x100 | Error at initialisation of the communication via the 2 byte PLC interface |
0x200 | error during communication |
0x300 | Timeout-Error. The permitted execution time was exceeded |
0x400 | Wrong parameter value at register number |
0x500 | Wrong parameter value at table number |
Example of a call in FBD:
IntfState AT%I* : PLCINTFSTRUCT;
IntfControl AT%Q* : PLCINTFSTRUCT;
CouplerReset1 : CouplerReset;
Start_CouplerReset : BOOL;
CouplerReset_Busy : BOOL;
CouplerReset_Err : BOOL;
CouplerReset_ErrId : UDINT;
The variables IntfState and IntfControl are linked with corresponding I/O variables in the TwinCAT System Manager.
Development environment |
Target system type |
PLC libraries to include (category group) |
TwinCAT v3.1.0 |
PC or CX (x86, x64, ARM) |
Tc2_Coupler (IO) |