Instruction List (IL)
An instruction list (IL) consists of a series of instructions. Each instruction begins in a new line and contains an operator and, depending on the type of operation, one or more operands separated by commas. In front of an instruction there can be an identification mark (label) followed by a colon (:).
A comment must be the last element in a line. Empty lines can be inserted between instructions.
Example:
LD     17
ST     lint     (* comment *)
GE     5
JMPC   next
LD     idword
EQ     istruct.sdword
STN    test
next:
Modifiers and operators in IL
In the IL language the following operators and modifiers can be used.
Modifiers:
Below you find a table of all operators in IL with their possible modifiers and the relevant meaning:
Operator
Modifiers
Meaning
LD
N
Make current result equal to the operand
ST
N
Save current result at the position of the Operand
S
Put the Boolean operand exactly at TRUE if the current result is TRUE
R
Put the Boolean operand exactly at FALSE if the current result is TRUE
AND
N, (
Bitwise AND
OR
N, (
Bitwise OR
XOR
Bitwise exklusive OR
ADD
Addition
SUB
Subtraction
MUL
Multiplication
DIV
Division
GT
GE
EQ
NE
LE
LT
JMP
CN
Jump to label
CAL
CN
call function block
RET
CN
Return from call of a function block
Evaluate deferred operation
You find a list of all IEC operators in the appendix.
Example of an IL program while using some modifiers:
LD     TRUE      (*load TRUE in the accumulator*)
ANDN   BOOL1     (*execute AND with the negated value of the BOOL1 variable*)
JMPC   label     (*if the result was TRUE, then jump to the label "label"*)
LDN    BOOL2     (*save the negated value of *)
ST     ERG       (*BOOL2 in ERG*)
label:
LD     BOOL2     (*save the value of *)
It is also possible in IL to put parentheses after an operation. The value of the parenthesis is then considered as an operand.
For example:
LD 2
MUL 2
ADD 3
ST Erg
Here is the value of Erg 7. However, if one puts parentheses:
LD 2
MUL( 2
ADD 3
ST Erg
Here the resulting value for Erg is 10, then the operation MUL is only then evaluated if you come to ")"; as operand for MUL 5 is then calculated.