Override and Stop
The override is used to change the target velocity of the axis online in the quickest possible way.
Stop is realized via override 0.0 and has priority over all other functions.
Override
The override is an instantaneous (not time-scaled) override, i.e. an attempt is made to reach the new velocity level as quickly as possible with the maximum permissible changes in acceleration.
The override can be changed from 0.0% to 100.0% in steps of 1/1,000,000.
There are four override types:
- The override refers to the target velocity level calculated and possibly reduced at axis start. If the new velocity level is not achievable, the old runtime table is maintained without notification.
 - The override refers to the target velocity specified by the user. If the new velocity level is not achievable, the old runtime table is maintained without notification.
 - The override refers to the target velocity level calculated and possibly reduced at axis start. If the new velocity level is not achievable then an attempt is made to achieve a smaller optimal velocity level.
 - The override refers to the target velocity specified by the user. If the new velocity level is not achievable then an attempt is made to achieve a smaller optimal velocity level.
The override is only activated if there is no stop and if the brake phase has not yet been reached. There is a possibility to start the axis with override 0%.
In case of excessively quick (especially periodical) changes of the overrides between two fixed velocity levels, the axis, whilst calculated deterministically, will behave indeterministically for the user.
Notes on the figures:
Scales: velocity [mm/s] / time [s]
Colors:
Set position: dark blue Actual position: light blue
Target velocity: dark green Actual velocity: light green
Set acceleration: dark red Actual acceleration: light red
Following error: yellow
Override changes: start override 100% -> 75% -> 100% (V = 2000.0 mm/s, from 0.0 mm to 5000.0 mm)
Override changes: start override 20% -> 100% (V = 2000.0 mm/s, from 0.0 mm to 5000.0 mm)
Stop
Stop is realized via override 0.0 and has - provided the brake phase has not yet been reached - priority over all other functions. If stop is requested and position compensation is active, compensation stop is activated simultaneously with the stop of the basic dynamics, in order to stop the axis as quickly as possible on the maximum permissible breaking ramp.
Emergency stop
In case of an emergency stop with parameters jerk R [mm/s/s/s] and deceleration A- [mm/s/s], the parameters jerk and deceleration are reset, if both parameter are genuinely larger than the parameters provided at the start. The stop is then initiated with the new parameters.