Target Position Monitoring
from TwinCAT V2.9 Build 1026
Command | TPM |
Cancellation | End of block |
The command 'TPM' is used to trigger target position monitoring from the NC program. At the end of the geometry this always leads to an accurate stop on the set value side and subsequent checking of the target position window. Block relaying takes place when the monitoring conditions are met for all axes in the group.
Like for PTP, this function is enabled and parameterized individually for each axis. This means that different limits can be selected for auxiliary axes than for the path axes, for example.
Sample 1:
N10 G01 X100 Y100 F6000
N20 G01 X300 Y100 TPM
At the end of the motion of N20, target position monitoring is performed both for the X axis and for Y axis (provided target position monitoring is enabled for both axes)
Sample 2:
N20 G01 X300 Y100
N30 M61 (Type Handshake)
N40 TPM
TPM can also be programmed in a dedicated block. In this case the last positioning is checked (of N20 in this case).
![]() | If target position monitoring is enabled for an axis, the target position alarm (PEH) should also be active. Time monitoring results in a channel error after the timeout (or before), if the axis is not yet in the target position window. In order to avoid unnecessary channel errors, a sufficiently large timeout value should be selected (e.g. 5 - 10 s). If no PEH time monitoring is active and the axis is permanently outside the position window, no block relaying takes place and the NC remains stationary when viewed from outside. The SEC is in Waiting state (not to be confused with Interpreter state). |
See also Accurate stop (G09)