FB_MBUdpReadWriteRegs (Modbus function 23)
This function first reads 1 to 128 output registers (16 bit) and then writes 1 to 128 output registers (16 bit).
sIPAddr : STRING(15);
nTCPPort : UINT:= MODBUS_TCP_PORT;
nUnitID : BYTE:=16#FF;
nReadQuantity : WORD;
nMBReadAddr : WORD;
nWriteQuantity : WORD;
nMBWriteAddr : WORD;
cbDestLength : UDINT;
pDestAddr : UDINT;
cbSrcLength : UDINT;
pSrcAddr : UDINT;
bExecute : BOOL;
tTimeout : TIME;
sIPAddr : Is a string containing the IP address of the target device.
nTCPPort : Port number of the target device.
nUnitID: Identification number of a serial sub-network device. If a device is addressed directly via TCP/IP, this value must be 16#FF.
nReadQuantity : Number of output registers (data words) to be read. The value of nReadQuantity must be > 0.
nMBReadAddr : Start address of the output registers to be read (word offset).
nWriteQuantity : Number of output registers (data words) to be written. The value of nWriteQuantity must be > 0.
nMBWriteAddr : Start address of the output registers to be written (word offset).
cbDestLength : Contains the max. byte size of the destination buffer. The minimum destination buffer byte size must be nReadQuantity * 2.
pDestAddr : Contains the address of the destination buffer into which the data are to be read. The buffer can be a single variable, an array or a structure, whose address can be found with the ADR operator.
cbSrcLength : Contains the max. byte size of the source buffer. The minimum source buffer byte size must be nWriteQuantity * 2.
pSrcAddr : Contains the address of the source buffer containing the data to be written. The buffer can be a single variable, an array or a structure, whose address can be found with the ADR operator.
bExecute: The function block is activated by a rising edge at this input.
tTimeout: States the length of the timeout that may not be exceeded by execution of the ADS command.
bBUSY : BOOL;
nErrId : UDINT;
cbRead : UDINT;
bBusy : When the function block is activated this output is set. It remains set until an acknowledgement is received.
bError : If an ADS error should occur during the transfer of the command, then this output is set once the bBusy output is reset.
nErrId : Supplies the ADS error number when the bError output is set.
cbRead: Contains the number of bytes currently read.
Function specific ADS error code  | Possible reason  |
0x8001  | Modbus function not implemented  |
0x8002  | Invalid address or length  |
0x8003  | Invalid parameters: - wrong number of registers  |
0x8004  | Modbus server error  |
Development environment  | Target system type  | PLC libraries to be linked  |
TwinCAT v2.8.0  | PC (i386)  | TcModbusSrv.Lib  |