MCV_CamSwitch
The MCV_CamSwitch function block realises the output of a cam-controlled switch that is assigned to an axis. The cam's range can be defined freely.
The function blocks internal calculations are based on a modulo coordinate system with the value range [0, 3600000] 0,1 µm or 10-4°.
The prerequisite that no more than half the modulo value range is covered by the axis in each PLC cycle must also be fulfilled.
Block diagram
MCV_CamSwitch 1:
Parameters of the function block
Axis
AXIS_REF
Axis reference.
Enable
Activates the cam-driven switch.
FirstOnPosition
DINT
Position of the axis at which the output of the cam-driven switch changes from FALSE to TRUE, if the axis is rotating in a positive direction.
Default unit [0,1µm or 10-4 °]
LastOnPosition
DINT
Position of the axis at which the output of the cam-driven switch changes from TRUE to FALSE, if the axis is rotating in a positive direction.
CompTime
DINT
Compensation time by which the switch-on phase of the cam-driven switch is advanced or delayed.
Unit [1ms]
PosType
INT
Selection whether command position or actual position of the axis should be used for comparison with the input variables and for calculation of the switch-on position / switch-off position that is changed by the compensation time.
0: Actual position of the axis (ACTIVE_POS)
1: Command position of the axis
(CURRENT_POS)
Active
Indicates the current state of the cam-driven switch.
State
Output of the cam-driven switch.
The output is TRUE, if:
Case 1:
‘FirstOnPosition’ < ‘LastOnPosition’
The value of the axis position lies between ‘FirstOnPosition’ and ‘LastOnPosition’.
Case 2:
‘ FirstOnPosition’ > ‘LastOnPosition’
The value of the axis position lies at time t0in front of and at the following time t1behind the range spanned by ‘FirstOnPosition’ and ‘LastOnPosition’ The signal remains for at least one PLC cycle at TRUE.
Error
Indicates if an error has occurred.
ErrorID
WORD
Error identification.
Pulsed
For visualization purposes. If "State" = TRUE, "Pulsed" is assigned TRUE for one second.
Case 1: ‘FirstOnPosition’<‘LastOnPosition’
MCV_CamSwitch 3:Fig.20: Behavior of the "State" output when ‘FirstOnPosition’ < ‘LastOnPosition’
Case 2: ‘FirstOnPosition’>‘LastOnPosition’
MCV_CamSwitch 4:Fig.21: Behavior of the "State" output when ‘FirstOnPosition’ < ‘LastOnPosition’