MC_MoveRelative
A relative motion is commanded with the MC_MoveRelative FB, in addition to the current position. This is regardless of whether the axis is in the ‘Discrete Motion’ or ‘Continuous Motion’ state. The motion is always executed jerk-limited with the constant set input ‘Jerk’. This value is valid for both ‘acceleration’ and ‘deceleration’.
Block diagram
Parameters of the FB
VAR_IN_OUT | |||
| Axis | AXIS_REF | Axis reference. |
VAR_INPUT | |||
| Execute | BOOL | Start the motion at rising edge. |
| Distance | LREAL | Relative distance for the motion. Range [-2147483648.0, 2147483647.0] |
| Velocity | LREAL | Value of the maximum velocity (always positive, not necessarily reached) Range [1.0, 2147483647.0] |
| Acceleration | LREAL | Value of the acceleration (always positive, increasing energy of the motor). Range [1.0, 2147483647.0] |
| Deceleration | LREAL | Value of the deceleration (always positive, decreasing energy of the motor). Range [1.0, 2147483647.0] |
| Jerk | LREAL | Value of the Jerk (always positive). Range [1.0, 2147483647.0] |
VAR_OUTPUT | |||
| Done | BOOL | The axis is within a range close to the target position. The range is specified by the parameter getriebe[...].window of the axis-specific machine data. |
| CommandAborted | BOOL | Command is aborted by another command. |
| Error | BOOL | Indicates if an error has occurred. |
| ErrorID | WORD | Error identification. |
Behavior of the FB
- This motion is commanded only when the axis is in the ‘Standstill’ or ‘Continuous Motion’ or ‘Discrete Motion’ or ‘Synchronized Motion’ state. If this is not the case, the ‘Error’ output is set to FALSE and ‘ErrorID’ indicates an error value that designates the state the axis is currently in.
- Within the FB, the ‘position’, ‘velocity’, ‘acceleration’, ‘deceleration’ and ‘jerk’ input variables are monitored only for their value range. If they are exceeded, an error number referring to the variable is output at the ‘ErrorID’ output and error is set to TRUE. Moreover, the maximum speed and acceleration data is limited within the motion controller. If speed values more than getriebe[0].dynamik.vb_max or ‘acceleration’ or ‘deceleration’ values more than getriebe[0].dynamik.a_max are commanded, the motion is nevertheless carried out, but the values are limited to the defined values and a warning 60211 or 60188 to 60194 is issued.
- Values that correspond to a minimum ramp time of TA (cycle time of the IPO, e.g. 2 ms) and a maximum ramp time of 100s make sense as the ‘Jerk’. The limit transition to non-jerk-limited speed realization lies at the minimum ramp time of TA. In the case of a value of 0, the maximum ramp time from the axis MDS is used to determine the ‘Jerk’.
- With this function block, active commands can be replaced with new commands and so the function block is retriggerable. The active command is thus aborted.
- If a non-referenced axis is commanded by this FB, the axis travels at the speed defined by the getriebe[...].vb_reflow parameter of the axis machine data.
- The positions of the software limit switches (kenngr.swe_pos, kenngr.swe_neg, kenngr.swe_toleranz) are monitored if the axis has been defined either as a linear or a rotary axis. This means that the kenngr.achs_typ of the axis machine data has the value 0x0001 or 0x0002. If the target position exceeds the position of the software limit switches as a result of commanding, the axis nevertheless starts off. If a software limit switch position is reached, the axis is braked, keeping to the defined acceleration.
