Realization of the FBs
The PLCopen FBs internally map the following state diagram.
The following state automaton in IEC 61131-3 structured text shows the framework for the realization of command issuing within an FB. The individual actions are in pseudo-code.
(* State automation for HLI assignment *)
CASE fb_state OF
FB_IDLE,
FB_ERROR:(* *)
IF ( tr_execute.Q = TRUE OR retry ) THEN
(* checking of the FB's input parameters *)
(* check whether transition is allowed *)
(* try to send the MC order. *)
(* IF (sendorder = OK) THEN fb_state := FB_ACTIVE; END_IF *)
END_IF
ACTIVE:(* *)
IF ( tr_execute.Q = TRUE OR retry) THEN
(* check whether FB's ax_ref connection has changed since idle state*)
(* try to send send the MC order. *)
END_IF
(* collection of Acknowledge *)
(* IF (Acknowledge = OK) THEN fb_state := FB_IDLE; END_IF *)
ELSE
(*// default: Unerlaubter Zustand *)
END_CASE;The FBs are not aware of any reset transition and, instead, after a preceding FB_ERROR following renewed triggering of the FB an attempt is simply mad to assert the new command issued. This is why, with respect to HLI command issuing, the state distributor does not distinguish between FB_IDLE and FB_ERROR.
The FB_RETRY state does not appears as an explicit state in the state distributor, but is kept in a variable in the states FB_IDLE,FB_ERROR and FB_ACTIVE in case the FB in the corresponding state cannot asset command issuing at first go.
The unique command number is kept as a global PLC data item and incremented by the FBs only at the time after successful command issuing from the FB_IDLE and FB_ERROR states, and is noted in its instance data.
When a command is issued out of the FB_ACTIVE state, a new command with the same command number is sent to the MC and an internal counter in the FB, which counts how many commands pertaining to one command number, is incremented.
This method dispenses with complex administration of the command numbers that have been issued and the associated acknowledgements received.
When an FB is triggered, it checks whether the station transition that would be triggered by execution of the FB in the FBSD is permitted at all in the momentary state of the FBSD ("transition allowed"). If this is not the case, the command is not sent at all and, instead, the FB reports a command issuing error (= error at FB level). In such a case, the axis state never changes because no command at all has been sent. You will find further information in the next section.