ADS Interface
All acyclic data are transferred with ADS Read, ADS Write, ADS ReadWrite or ADS Write Control to a BACnet device, a notification sink, a BACnet server or a BACnet client. Each BACnet device has a dedicate Net ID, which is displayed via the Settings tab and supports the following ports:
Port | Description |
0xFFFF | Addresses the BACnet device itself, i.e. data that are not specific for a BACnet server, a notification sink or a BACnet client |
1000 - 8192 | Addresses a BACnet server, a notification sink or a BACnet client. The first configured BACnet server/client can be reached via port 1000, the second via port 1001 etc. Deleting a BACnet server/client does not lead to shifting of the ports, i.e. the assignment of the ADS port can therefore not necessarily be deduced from the order in the System Manager. The respective port can be viewed via the Settings tab of a BACnet server/client. |
ADS-Read
An overview of the IndexGroup/IndexOffset supported by a BACnet device for ADS Read is provided below.
IndexGroup with local addressing of the BACnet device (port 0xFFFF)
IndexGroup (Lo-Word) | IndexGroup (Hi-Word) | IndexOffset | Description |
0x0006 | 0x8000 | always 0 | Starting a scan for other BACnet devices in the network. |
0x0008 | 0x8000 | always 0 | Stopping a scan for other BACnet devices in the network. Preparation for reading the results list. |
0x0007 | 0x8000 | 0 : Number of entries in the results list (number of clients*2) 2*n: IP address of device n 2*n+1: Device ID of device n 0xffffffff | A scan with the aid of a BACnet device follows the following pattern:
The scan results are read via this IndexGroup. The number of entries in the results list can be determined via IndexOffset 0. This corresponds to twice the number of BACnet devices found in the network. Even IndexOffsets > 0 address the IP address of a device; odd IndexOffsets address the device ID. Before reading the results list the scan process has to be stopped. If, for example, 2 devices are found in a network, the query for index 0 comes up with 4. IndexOffset 1 relates to the device ID of device 1, IndexOffset 2 the IP address of device 1, IndexOffset 3 the device ID of device 2 and IndexOffset 4 the IP address of device 2. enum BACnetAddressChoice struct BACnetAddress struct BACnetScanResult |
0x000A | 0x8000 | always 0 | Starting a backup. (triggering the BACnet service Backup Start) |
0x001A | 0x8000 | always 0 | Stopping a backup. (triggering the BACnet service Backup End) Between Backup Start and End the generated backup files can be saved with the aid of the Property Configuration Files of device object and the ADS file service. |
0x002A | 0x8000 | always 0 | Starting a restore. (triggering the BACnet service Restore Start) |
0x003A | 0x8000 | always 0 | Stopping a restore (triggering the BACnet service Restore End) |
0x004A | 0x8000 | always 0 | Aborting a restore (triggering the BACnet service Restore Abort). |
0x005A | 0x8000 | always 0 | Restarting the TwinCAT computer (triggering the BACnet service Cold Start) |
0x006A | 0x8000 | always 0 | Restarting TwinCAT (triggering the BACnet service Warm Start). |
0x000C | 0x8000 | always 0 | Reading the supplement key status:
0x000D | 0x8000 | always 0 | Reading the current Foreign Device Table (FDT) as array of type FDTEntry: struct FDTEntry |
0x000E | 0x8000 | always 0 | Reading the current Broadcast Distribution Table (BDT) as array of type BDTEntry: struct BDTEntry |
0x000F | 0x8000 | always 0 | Reading the BACnet diagnosis in the form of BACnetDiagnosis. (see BACnet device tab Diagnostics). |
0x001F | 0x8000 | always 0 | Reading the Advanced Parameters in the form of Advanced Parameters struct AdvancedParameters |
IndexGroup for addressing a BACnet server/client (port 1000-8191) - property access
Property specific ADS services can be used with an IndexGroup/IndexOffset with the following scheme:
- Bit 0-21 contains the property ID of the required BACnet property
- Bit 22-30 contains the group type describing the respective functionality
- Bit 31 is always 1 and activates the group type mode for using the property-specific services
- The IndexOffset contains the object ID of the required object
IndexGroup | IndexOffset | Description |
0x80000000 + property ID Group type (bits 22-30): 0 | Object ID
| Reading the current data of a property. Example: The property PresentValue of object BinaryInput: 42 can be read via IndexGroup: 0x80000055 and IndexOffset: 0x00C0002A. |
0x80400000 + property ID Group type (bits 22-30): 1 | Object ID
| Reading the BACnet data type of a property. A list of data type coding can be found in the appendix. |
0x80800000 + property ID Group type (bits 22-30): 2 | Object ID
| Reading the data length of the current property value. |
0x80C00000 + property ID Group type (bits 22-30): 3 | Object ID
| Reading the write protection status of a property. The read data are interpreted as follows:
0x81400000 + property ID Group type (bits 22-30): 5 | Object ID
| Reading the number of elements of list and array types. |
IndexGroup for addressing a BACnet server (port 1000-8191)
0x82400000 | 0 number of list entries > 0 and < 0xffffffff | Reading the objects present in the server. The objects created on a server can also be determined by reading the property ObjectList of the device object. Index 0: Number of entries |
0x83400000 | always 0 | Reading the list of dynamically created objects. For each object the list has a 4-byte entry containing the respective object ID. |
IndexGroup for addressing a notification sink (port 1000-8191)
0x00000001 | always 0 | Reading the current number of event notifications in the event notification buffer |
0x00000002 | always 0 | Reading the current number of COV notifications in the COV notification buffer |
0x00000003 | Number of the event notification (0 .. number-1) | Reading an event notification. The structure of event notifications can be determined in the online dialog of the notification sink. |
0x00000004 | Number of the COV notification (0 .. number-1) | Reading a COV notification. The structure of COV notifications can be determined in the online dialog of the notification sink. |
0x00000005 | Number of the event notification (0 .. number-1) | Deleting an event notification |
0x00000006 | Number of the COV notification (0 .. number-1) | Deleting a COV notification |
0x00000007 | Number of the event notification (0 .. number-1) | Reading the time of receipt of an event notification |
0x00000008 | Number of the COV notification (0 .. number-1) | Reading the time of receipt of a COV notification |
ADS Write
An overview of the IndexGroup/IndexOffset supported by TwinCAT BACnet/IP for ADS Write is provided below.
0x8000002D | always 0 | Triggering a global broadcast UTC synchronisation. A valid BACnetDateTime time stamp is required. struct BACnetTime { BYTE hour; BYTE minute; BYTE second; BYTE hundredths; } structBACnetDate { BYTE year; BYTE month; BYTE day; BYTE dayOfWeek; } structBACnetDateTime { BACnetDate date; BACnetTime time; } |
0x8000000F | always 0 | BACnet diagnosis control: Transferred data size 4:
Data size not equal 4: resetting the BACnet diagnosis |
0x8000000E | always 0 | Writing the Broadcast Distribution Table (BDT) as array in the form of BDTEntry: struct BDTEntry |
Property specific ADS services can be used with an IndexGroup with the following scheme:
- Bits 0-21 contains the property ID of the required BACnet property
0x80000000 + property ID | Object ID
| Writing a property value. Prioritized write access is available via bits 22-30 of the IndexGroup. Priority 1 (top priority in BACnet) can be defined via the value 0x010 in bits 22-30. Priority 16 (the lowest priority in BACnet) can be defined with value 0x100. |
0x84000000 + property-ID | Object ID
| Write access with priority 1. |
0xC0000000 + property ID | Object ID
| Write access with priority 16. |
0x80800000 | always 0 | Creating an object dynamically. The following data must be transferred in the write request, to parameterize the object creation:
0x81000000 | always 0 | Deleting a dynamically created object. The following data must be transferred in a write request:
0x80C00000 | always 0 | Triggering saving of the persistent data. Only valid for BACnet servers if Persist Online Data is active. |
ADS-ReadWrite
An overview of the IndexGroup/IndexOffset supported by TwinCAT BACnet/IP for ADS ReadWrite is provided below.
0x82C00000 | Object ID
| Reading the property list of an object. This service consolidates all properties of an object, like the BACnet service ReadPropertyMultiple. When the ADS ReadWrite command is executed a list with the required properties must be transferred. Currently only triggering of the complete list is supported. To this end 4 bytes with the value 0x00000008 must be transferred. |
0x8B800000 | always 0 | Query of the object ID with the name of an object. The name of the requested object must be written as ASCII string. The corresponding object ID (4 bytes) is returned. If an object is not found the ADS error NOT_FOUND is returned. |
ADS Error Codes
The 32-bit ADS error code always consists of a general ADS error code (low word, see ADS documentation). The appropriate text message will also be displayed in the TwinCAT System Manager Logger.