FB_BACnet_Schedule_EX
FB_BACnet_Schedule_EX 1:
Application
The function block FB_BACnet_Schedule_EX can be used for read and write access to a BACnet object of type Schedule.
VAR_OUPUT
bReady         : BOOL;
bPresentValue  : BOOL;
bOverridden    : BOOL;
bOutOfService  : BOOL;
bFault         : BOOL;
bInAlarm       : BOOL;
bConfigError   : BOOL;
bOtherFault    : BOOL;
tObjectID      : T_BACnet_ObjectIdentifier:=16#FFFFFFFF;
bError         : BOOL;
nErrorId       : UINT;
bReady: Notification of general readiness. If this output is set, the other status outputs are valid (PresentValue, Overridden ...). If the output is FALSE, the corresponding function block FB_BACnet_Device does not report "Operational", or the block instance was not linked correctly in the TwinCAT System Manager.
bPresentValue: Current value of the BACnet object (see also BACnet specification DIN EN ISO 16484-5 for BACnet object Schedule and property Present_Value).
bOverridden, bOutOfService, bFault, bInAlarm: See BACnet specification DIN EN ISO 16484-5 for BACnet object Schedule and property Status_Flags.
bConfigError, bOtherFault: See BACnet specification DIN EN ISO 16484-5 for BACnet object Schedule and property Reliability.
tObjectID: Object ID of the BACnet object (object type and object instance).
bError: An error is pending.
nErrorId: see global constants BACnet_Globals.
Device         : FB_BACnet_Device;
Device: Specification of the instance of the local corresponding BACnet server block. For each BACnet adapter one BACnet server is possible. See FB_BACnet_Adapter and FB_BACnet_Device for further information.