BAC_AC_SpRmTH_03
Application
The template BAC_AC_SpRmTH_02 is a set value program for an air conditioning plant with room or extract air cascade control for temperature and humidity.
There are two basic room temperature set values (SpTHtgY1, SpTColY1), with an energy-neutral zone between the lower set value (heating mode) and the upper set value (cooling mode). The energy-neutral zone is monitored via the function SpHSupVis.
An outside temperature-dependent offset of the basic room temperature set values is realised via two curve functions (summer/winter compensation).
The relative room humidity set value (%) is entered with BACnet AV object SpH.
There is no energy-neutral zone between a lower set value (humidification) and an upper set value (dehumidification) for humidity control.
The set value for the relative room humidity SpH is converted into a set value for the absolute room humidity (g/kg) SpX within the template via the current room temperature.
Interface
System diagram
Block diagram
VAR_Input
rRmT : REAL;
rRmT: Measured value of the room temperature
rSpTHtg : REAL;
rSpTCol : REAL;
rSpX : REAL;
rSpH : Real;
rSpTHtg: Calculated heating set value for the room temperature
rSpTCol: Calculated cooling set value for the room temperature
rSpX: Calculated set value of the absolute room humidity
rSpH: Set value for the relative room humidity
Program description
Instance | Type | Task |
SpTColX1 | Input of the value for interpolation point SpTColX1 cooling | |
SpTColX2 | Input of the value for interpolation point SpTColX2 cooling | |
SpTColY1 | Input of the value for interpolation point SpTColY1 cooling. The value is the base cooling setpoint value | |
SpTColY2 | Input of the value for interpolation point SpTColY2 cooling | |
SpTColScale | The function block calculates the characteristic cooling set value curve for the current room temperature, depending on the outside temperature.
SpTCol | Output of the calculated room temperature cooling set value | |
SpTHtgX1 | Input of the value for interpolation point SpTHtgX1 heating | |
SpTHtgX2 | Input of the value for interpolation point SpTHtgX2 heating | |
SpTHtgY1 | Input of the value for interpolation point SpTHtgY1 heating. The value is the base heating setpoint value | |
SpTHtgY2 | Input of the value for interpolation point SpTHtgY2 heating | |
SpTHtgScale | The function block calculates the characteristic heating set value curve for the current room temperature, depending on the outside temperature.
SpTHtg | Output of the calculated room temperature heating set value | |
SpTSupVis | The function block is used for controlling the energy-neutral zone between the two set values SpTCol and SpTHtg | |
SpH | Input of the set value for the relative room humidity (%). | |
SpHX | This function block is used to calculate the set value for the absolute room humidity. For calculating the value, the room temperature, the set value for the relative humidity SpH and the barometric air pressure are required. | |
SpX | Output of the calculated absolute room humidity set value (g/kg). |
Version history
Version number | Comments |
1.0.1 | First release |