FB_BA_SpRmT
Formation of room temperature setpoints
Functional description
The function block FB_BA_SpRmT assigns setpoints for cooling and heating operation to each of the energy levels Protection, Economy, PreComfort and Comfort.
The following graphics illustrates the behaviour of the function block; the entered values should be regarded as examples:
The value lrShiftHeating is applied to the Comfort and Precomfort values for the heating mode as central setpoint shift. In addition, winter compensation lrWinCpsn is applied.
Similarly, the following applies for the cooling mode: The value lrShiftCooling is applied to the Comfort and Precomfort values. In addition, the summer compensation value lrSumCpsn is applied.
Auto-correction
The setpoint shift is intended for small corrections of the values. Although it is possible to enter any input values, a heating system will only work in a meaningful manner if the setpoints have ascending values in the following order:
- Protection Heating
- Economy Heating
- Precomfort Heating
- Comfort Heating
- Comfort Cooling
- Precomfort Cooling
- Economy Cooling
- Protection Cooling
The auto-correction is based on the principle that, starting from the value for Economy Heating, the system checks whether this value is smaller than the next lower parameter, in this case Protection Heating. If this is the case, the value for Economy Heating is adjusted to match the value for Protection Heating. The system then checks whether the value for Precomfort Heating is less than Economy Heating and so on, until the value for Protection Cooling is compared with the value for Economy Cooling. If one or several values were corrected, this is indicated with a TRUE signal at output bValCorr.
Inputs/outputs
lrPrtcHtg : LREAL;
lrEcoHtg : LREAL;
lrPreCmfHtg : LREAL;
lrCmfHtg : LREAL;
lrCmfCol : LREAL;
lrPreCmfCol : LREAL;
lrEcoCol : LREAL;
lrPrtcCol : LREAL;
lrShiftHtg : LREAL;
lrShiftCol : LREAL;
lrSumCpsn : LREAL;
lrWrWinCpsn : LREAL;
bValCorr: autocorrection: at least one of the resulting setpoints was adjusted such that the values continue to monotonically increase.
lrPrtcHtg : basic Protection Heating setpoint
lrEcoHtg: basic Economy Heating setpoint
lrPreCmfHtg: basic PreComfort Heating setpoint
lrCmfHtg: basic Comfort Heating setpoint
lrCmfCol: basic Comfort Cooling setpoint
lrPreCmfCol: basic PreComfort Cooling setpoint
lrEcoCol: basic Economy Cooling setpoint
lrPrtcCol : basic Protection Cooling setpoint
lrShiftHtg : setpoint value shift heating
lrShiftCol: setpoint value shift cooling
lrSumCpsn: value summer compensation
lrWinCpsn: value winter compensation
lrPrPrtcHtg : LREAL;
lrPrEcoHtg : LREAL;
lrPrPreCmfHtg : LREAL;
lrPrCmfHtg : LREAL;
lrPrPrtcCol : LREAL;
lrPrEcoCol : LREAL;
lrPrPreCmfCol : LREAL;
lrPrCmfCol : LREAL;
stPrSp : ST_BA_SpRmT;
lrPrPrtcHtg : resulting Protection Heating setpoint
lrPrEcoHtg: resulting Economy Heating setpoint
lrPrPreCmfHtg: resulting PreComfort Heating setpoint
lrPrCmfHtg: resulting Comfort Heating setpoint
lrPrCmfCol: resulting Comfort Cooling setpoint
lrPrPreCmfCol: resulting PreComfort Cooling setpoint
lrPrEcoCol: resulting Economy Cooling setpoint
lrPrPrtcCol : resulting Protection Cooling setpoint
stPrSp: consolidated output of the resulting values in a structure.
Development environment | Target system | required library | required supplement |
TwinCAT 2.11 R3/x64 | PC/CX | TcBA library from V1.0.0 | TS8040 | TwinCAT Building Automation from V1.0.0 |