PLC
ANY and ANY_<type>
When implementing a function or a method, you can declare inputs (VAR_INPUT) as variables with a generic IEC data type (ANY or ANY_<type>). Consequently you can implement calls whose call parameters differ by their data type.
At runtime you can query the value transferred and its data type via a predefined structure within the programming block for the input variable.
An input of the data type ANY or ANY_<type> cannot be assigned a constant when calling the function or method.
The generic IEC data types shown below are supported. The table shows which generic data type allows which elementary data types.
Generic data types
Elementary data types
ANY
ANY_BIT
BYTE, WORD, DWORD, LWORD
ANY_DATE
DATE_AND_TIME, DT, DATE, TIME_OF_DAY, TOD
ANY_NUM
ANY_REAL
REAL, LREAL
ANY_INT
USINT, UINT, UDINT, ULINT
SINT, INT, DINT, LINT
ANY_STRING
STRING, WSTRING
Predefined structure
When the code is compiled, an ANY data type is replaced internally with the following structure:
TYPE AnyType :
STRUCT
    // the type of the actual parameter
    typeclass : __SYSTEM.TYPE_CLASS ;
    // the pointer to the actual parameter
    pvalue : POINTER TO BYTE;
    // the size of the data, to which the pointer points
    diSize : DINT;
END_STRUCT
END_TYPE
The actual call parameter is then assigned to the structure elements at runtime.
Sample 1: Transfer of elementary data types to inputs with a generic data type
The transfer parameters of the function calls have different data types.
FUNCTION F_AnyBitFunc : BOOL
    value : ANY_BIT;
FUNCTION F_AnyDateFunc : BOOL
    value : ANY_DATE;
FUNCTION F_AnyFunc : BOOL
    value : ANY;
FUNCTION F_AnyIntFunc : BOOL
    value : ANY_INT;
FUNCTION F_AnyNumFunc : BOOL
    value : ANY_NUM;
FUNCTION F_AnyRealFunc : BOOL
    value : ANY_REAL;
FUNCTION F_AnyStringFunc : BOOL
    value : ANY_STRING;
PROGRAM MAIN
    bBOOL            : BOOL           := TRUE;
    nBYTE            : BYTE           := 16#AB;
    nWORD            : WORD           := 16#1234;
    nDWORD           : DWORD          := 16#6789ABCD;
    nLWORD           : LWORD          := 16#0123456789ABCDEF;
    sSTRING          : STRING         := 'xyz';
    wsWSTRING        : WSTRING        := "abc";
    dtDATEANDTIME    : DATE_AND_TIME  := DT#2017-02-20-11:07:00;
    dDATE            : DATE           := D#2017-02-20;
    tdTIMEOFDAY      : TIME_OF_DAY    := TOD#11:07:00;
    fREAL            : REAL           := 42.24;
    fLREAL           : LREAL          := 24.42;
    nUSINT           : USINT          := 12;
    nUINT            : UINT           := 1234;
    nUDINT           : UDINT          := 12345;
    nULINT           : ULINT          := 123456;
    nSINT            : SINT           := -12;
    nINT             : INT            := -1234;
    nDINT            : DINT           := -12345;
    nLINT            : LINT           := -123456;
F_AnyFunc(bBOOL);
F_AnyFunc(nBYTE);
F_AnyFunc(nWORD);
F_AnyFunc(nDWORD);
F_AnyFunc(nLWORD);
F_AnyFunc(sSTRING);
F_AnyFunc(wsWSTRING);
F_AnyFunc(dtDATEANDTIME);
F_AnyFunc(tdTIMEOFDAY);
F_AnyFunc(fREAL);
F_AnyFunc(fLREAL);
F_AnyFunc(nUSINT);
F_AnyFunc(nUINT);
F_AnyFunc(nUDINT);
F_AnyFunc(nULINT);
F_AnyFunc(nSINT);
F_AnyFunc(nINT);
F_AnyFunc(nDINT);
F_AnyFunc(nLINT);
F_AnyBitFunc(nBYTE);
F_AnyBitFunc(nWORD);
F_AnyBitFunc(nDWORD);
F_AnyBitFunc(nLWORD);
F_AnyStringFunc(sSTRING);
F_AnyStringFunc(wsWSTRING);
F_AnyDateFunc(dtDATEANDTIME);
F_AnyDateFunc(dDATE);
F_AnyDateFunc(tdTIMEOFDAY);
F_AnyNumFunc(fREAL);
F_AnyNumFunc(fLREAL);
F_AnyNumFunc(nUSINT);
F_AnyNumFunc(nUINT);
F_AnyNumFunc(nUDINT);
F_AnyNumFunc(nULINT);
F_AnyNumFunc(nSINT);
F_AnyNumFunc(nINT);
F_AnyNumFunc(nDINT);
F_AnyNumFunc(nLINT);
F_AnyRealFunc(fREAL);
F_AnyRealFunc(fLREAL);
F_AnyIntFunc(nUSINT);
F_AnyIntFunc(nUINT);
F_AnyIntFunc(nUDINT);
F_AnyIntFunc(nULINT);
F_AnyIntFunc(nSINT);
F_AnyIntFunc(nINT);
F_AnyIntFunc(nDINT);
F_AnyIntFunc(nLINT);
Sample 2: Comparison of two transferred variables
The function compares the two variables transferred to determine whether they are of the same type and have the same value.
FUNCTION F_GenericCompare : BOOL
    any1 : ANY;
    any2 : ANY;
    nCount: DINT;
IF any1.typeclass <> any2.typeclass THEN
   RETURN;
END_IF
IF any1.diSize <> any2.diSize THEN
    RETURN;
END_IF
// Byte comparison
FOR nCount := 0 TO any1.diSize-1 DO
    IF any1.pvalue[nCount] <> any2.pvalue[nCount] THEN
        RETURN;
    END_IF
END_FOR
F_GenericCompare := TRUE;
Sample 3: Determination of the data type transferred
The function checks whether the variable transferred is of the type REAL or LREAL. If this is the case, the value of the variable is rounded.
// function to round transfer parameters of the type REAl and LREAL (other types are detected as invalid)
FUNCTION F_RoundFloatingValue : INT
    anyIn        : ANY;               // input variable of the type ANY
    pAnyReal     : POINTER TO REAL;   // pointer to a variable of the type REAL
    pAnyLReal    : POINTER TO LREAL;  // pointer to a variable of the type LREAL
    bInvalidType : BOOL;              // output variable with value TRUE if the transferred parameter has an invalid type
// round floating value for a transfer parameter of the type REAL
IF (anyIn.TypeClass = __SYSTEM.TYPE_CLASS.TYPE_REAL) THEN
    pAnyReal              := anyIn.pValue;
    F_RoundFloatingValue  := REAL_TO_INT(pAnyReal^);
// round floating value for a transfer parameter of the type LREAL
ELSIF (anyIn.TypeClass = __SYSTEM.TYPE_CLASS.TYPE_LREAL) THEN
    pAnyLReal             := anyIn.pValue;
    F_RoundFloatingValue  := LREAL_TO_INT(pAnyLReal^);
// inform about invalid type if the transfer parameter is not of the type REAL or LREAL
ELSE
    bInvalidType          := TRUE;
END_IF