Configuring CPU cores
Using the real-time node TIRS, you can read the CPU cores of a target system and configure the distribution between Windows and TwinCAT real time (core isolation). If cores are re-isolated, the target system must be restarted. However, this restart is triggered only if the desired distribution is not already active on the target system.
ITcSysManager2is available forSetTargetNetId.- Administrator rights are available on the target system.
- The target system must be online (accessible) for the transfer.
Recommended procedure
- 1. Determine available cores (optional): When an online connection is established,
ProduceXmlon theTIRSnode returns<AvailabeCPUs>, which specifies the number of cores on the target system.MaxCPUscorresponds exactly to this core count, because the available cores are distributed. - 2. Set the configuration: Set
MaxCPUsandAffinityto the desired distribution yourself (see the bitmask table below). Optionally, you can addCPUsfor detailed parameters. - 3. Apply: Add
<SetOnTarget>and<RequestReboot>to a<Methods>block and write it usingConsumeXml.
What each element does
Item | Effect |
| Select which cores the real time system will use, and enable them. The value is a hexadecimal bit mask (see below). This is what actually activates the cores. |
| Optional. Configures detailed parameters ( |
| Transfers the configuration to the target system. |
| Requests the restart required for isolation. |
Important note
<Affinity>is required to activate cores. The<CPU id="…"/>entries do not enable any cores; they only configure those that are already enabled. If a core is listed in<CPUs>but is not enabled via<Affinity>, the import will fail with the message “Cpu is not enabled!”.MaxCPUs,Affinityand the<CPU>entries must match.MaxCPUsis the total number of cores in the target system.<Affinity>selects from among them the cores used by the real-time system. Each<CPU id="i">entry must refer to one of the cores activated via<Affinity>.SetOnTargetandRequestRebootonly apply if a reconfiguration is necessary. The transfer and restart will only take place if the target system does not already provide the requested core distribution. If a distribution is requested that is already active on the target system, the system will not restart.SetOnTargetandRequestRebootmust be included in the<Methods>block. If the<Methods>block is missing, the transfer and restart will not be triggered. The values will then remain as project settings.- Always specify the complete configuration (
MaxCPUsandAffinity), not justMaxCPUsand not just the<CPU>entries. This is the only way to ensure that the desired change is reliably detected and applied.
Complete sample: 3 shared cores and 1 isolated core (4-core system)
ITcSysManager2 sysMan2 = (ITcSysManager2)sysManager;
sysMan2.SetTargetNetId("192.168.1.100.1.1");
ITcSmTreeItem realtimeSettings = sysMan2.LookupTreeItem("TIRS");
// Optional: read the number of available cores on the target system
string current = realtimeSettings.ProduceXml()
// When online, the result contains e.g. <AvailabeCPUs>4</AvailabeCPUs>
// (the MaxCPUs/Affinity values in it are the project state and must be set explicitly)
// Set the configuration and apply it to the target system:
// MaxCPUs = 4 cores in total on the target, 1 of them isolated (NonWindowsCPUs="1")
// Affinity = activates all 4 cores (bits 0..3 = #x...0f)
string xmlApply = @"<TreeItem>
<RTimeSetDef>
<MaxCPUs NonWindowsCPUs=""1"">4</MaxCPUs>
<Affinity>#x000000000000000f</Affinity>
<Methods>
<SetOnTarget>true</SetOnTarget>
<RequestReboot>true</RequestReboot>
</Methods>
</RTimeSetDef>
</TreeItem>";
realtimeSettings.ConsumeXml(xmlApply);After the restart, the application must resume at the appropriate point.
You can check in advance whether a SetOnTarget will actually result in a reconfiguration with a restart using <CpuConfigValidOnTarget> in the ProduceXml result. This value does not indicate whether the distribution matches exactly, but rather whether the configuration specified in the project is covered by the configuration already active on the target system. If the value is 1 (true), the configuration is already covered, and no changes or restart are necessary. If the value is 0 (false), a SetOnTarget would reconfigure and restart the target system. The RT cores set via <Affinity> are the ones that matter here, not the numbers in the fields for shared and isolated cores. This mechanism prevents a ConsumeXml from accidentally triggering an unnecessary restart.
Meaning of TargetCPUInfo in the ProduceXml result
Within <RTimeSetDef>, ProduceXml returns a <TargetCPUInfo> block. It describes the target system's CPU and the mapping between the project and the target system. The values come from the connected device and are therefore only included in the XML if the target system is online (accessible).
<TargetCPUInfo>
<RealTimeCPUs>2</RealTimeCPUs>
<CPUFamily>6</CPUFamily>
<CPUFrequency>1498</CPUFrequency>
<CPUType>86</CPUType>
<AvailabeCPUs>2</AvailabeCPUs>
<NumProcessors>1</NumProcessors>
<CpuConfigValidOnTarget>true</CpuConfigValidOnTarget>
<RTimeCapabilities>1</RTimeCapabilities>
</TargetCPUInfo>Item | Meaning |
<RealTimeCPUs>
| The number of cores selected as RT-cores – that is, the cores checked in the RT-Core column of the core list in the real time settings (real-time, settings tab). If two cores are checked there, the XML will contain <RealTimeCPUs>2</RealTimeCPUs>. This corresponds to the number of bits set via <Affinity>. It is not the number of isolated cores – that is specified in the NonWindowsCPUs attribute of <MaxCPUs>. |
<CPUFamily>
| Processor family based on the manufacturer identifier. For virtually all modern Intel® processors (Core i3/i5/i7, Atom®, Xeon®), the value is 6. |
<CPUFrequency> | Processor clock frequency in MHz. |
<CPUType>
| Processor architecture. 86 stands for x86/x64, which refers to a standard industrial PC. Target systems with a different architecture (e.g., Arm®-based devices) report a different value here. |
<AvailabeCPUs> | Number of cores in the target system to be distributed – the only reliable value for the actual number of cores (see note above). The spelling without the second “l” is the actual name used in the XML. |
<NumProcessors> | Number of physical processors (packages/sockets), not cores. In the sample above: a processor with two cores. |
<CpuConfigValidOnTarget> | Indicates whether the project configuration is already covered by the distribution active on the target system – and thus whether a SetOnTarget operation would trigger a restart (see the section above). |
<RTimeCapabilities> | A metric for the target system's real time capabilities. This value is not required for the core configuration via ConsumeXml. |
<CPUType> and <CPUFamily> are essentially fixed identifiers for “x86 PC with a modern Intel® processor”, it is normal for them not to change when the core configuration is modified. The following are relevant: <AvailabeCPUs> (available cores), <RealTimeCPUs> (cores selected as RT cores), and <CpuConfigValidOnTarget> (whether a restart is required or not).
Affinity bitmask
<Affinity> is a hexadecimal bitmask. Bit i represents the core with id="i":
Cores used | Affinity |
Core 0 |
Core 0 to 1 |
Core 0 to 2 |
Core 0 to 3 |
Core 0 to 5 |
Core 0 to 7 |
Configuring detailed parameters for each core
ITcSmTreeItem realtimeSettings = systemManager.LookupTreeItem("TIRS");
string xml = @"<TreeItem>
<RTimeSetDef>
<MaxCPUs>3</MaxCPUs>
<Affinity>#x0000000000000007</Affinity>
<CPUs>
<CPU id=""0"">
<LoadLimit>10</LoadLimit>
<BaseTime>10000</BaseTime>
<LatencyWarning>200</LatencyWarning>
</CPU>
<CPU id=""1"">
<LoadLimit>20</LoadLimit>
<BaseTime>5000</BaseTime>
<LatencyWarning>500</LatencyWarning>
</CPU>
<CPU id=""2"">
<LoadLimit>30</LoadLimit>
<BaseTime>3333</BaseTime>
<LatencyWarning>1000</LatencyWarning>
</CPU>
</CPUs>
</RTimeSetDef>
</TreeItem>";
realtimeSettings.ConsumeXml(xml);<Affinity>#x0000000000000007</Affinity> enables cores 0 through 2, corresponding to the three <CPU> entries. Without the <Methods> block, this remains merely a project setting. To transfer the data to the target system, add <SetOnTarget> and <RequestReboot> .
Setting the task CPU affinity
ITcSmTreeItem tasks = systemManager.LookupTreeItem("TIRT");
ITcSmTreeItem task1 = tasks.CreateChild("TaskA", 1);
task1.ConsumeXml(@"<TreeItem>
<TaskDef>
<CpuAffinity>#x0000000000000001</CpuAffinity>
</TaskDef>
</TreeItem>");The affinity is a hexadecimal bitmask. Core 0 corresponds to #x0000000000000001 , Core 1 corresponds to #x0000000000000002 , Core 2 corresponds to #x0000000000000004, and so on.