SCT24xx | General
Primary side | SCT24xx-xxxx |
Thermal rated continuous current Icth | ≤2000 A: 1,2 * IN >2000 A: 1,0 * IN |
Rated short-time thermal current Ith | 60 * IN /1 s (max. 100 kA) |
Rated impulse current Idyn | 2,5 * Ith |
Rated frequency fR | 50..60 Hz |
Secondary side | SCT24xx-xxxx |
Secondary rated current Isr | 1 A |
Overcurrent limiting factor | FS5 |
Operating conditions | SCT24xx-xxxx |
Permissible ambient temperature range during operation | -5…+50 °C |
Permissible ambient temperature range during storage | -25 … +70 °C |
Permissible relative humidity | 5 … 85 % |
Operating height | Up to 1000 m |
Protection class | IP20 |
Insulation characteristics | SCT24xx-xxxx |
Rated insulation level Um | 1,2/6/- kV |
Surge voltage resistance according to DIN EN 61439 1:2012-06 | 12 kV (1,2/50 µs) |
Insulation class | E |
General data | SCT24xx-xxxx |
Max. Diameter conductor bushing primary conductor | 43,7 mm |
Rail dimensions primary conductor | 63 mm x 10 mm / 50 mm x 30 mm |
Connection technology secondary | CAGE CLAMP ® |
Conductor cross section secondary | 2,5 … 4 mm² / 14-12 AWG |
Stripping length | 9 – 10 mm / 0,37 in |
Size | 4 |
Dimensions (W x H x D) | 95 mm x 115 mm x 52 mm |
Weight | 470 g |
Markings, standards and regulations *) | SCT24xx-xxxx |
Markings/Approvals | CE, EAC, UKCA |
Flame rating | UL 94 V-0 |
Standards/Regulations | IEC 61869-1; IEC 61869-2 |
SCT24xx dimensions, size 4
Fig.23: Isometric view, top view; all dimensions in mm
Fig.24: Right side view, front view, left side view; all dimensions in mmConductor bushing of the primary conductor, size 4 | |
Rail 1 [mm] | 63 x 10 |
Rail 2 [mm] | 50 x 30 |
Rail 3 [mm] | / |
Round conductor [mm] | Ø 43,7 |