Safety and protection features
Insulation resistance
Min. 500 MOhm
In the delivery state between input and output, measured with 500 Vdc
Min. 500 MOhm
In the delivery state between input and Chassis Ground, measured with 500 Vdc
Min. 500 MOhm
In the delivery state between output and Chassis Ground, measured with 500Vdc
Min. 500 MOhm
In the delivery state between output and DC‑OK contacts, measured with 500 Vdc
PE resistance
Max. 0.1 Ohm
Resistance between PE terminal and the housing in the area of the DIN rail mounting bracket.
Output overvoltage protection
Typ. 31 Vdc
Max. 32.5 Vdc
In case of an internal defect, a redundant circuit limits the maximum output voltage. The output shuts down and automatically attempts to restart.
Class of protection
I
According to IEC 61140
Degree of protection
IP20
According to EN/IEC 60529
Over-temperature protection
Not included
Input transient protection
MOV (Metal Oxide Varistor)
For protection values see chapter “EMC
Internal input fuse
Included
Not user replaceable slow-blow high-braking capacity fuse
Touch current (leakage current)
The leakage current, which is produced by the DC/DC converter itself, depends on the input voltage ripple and need to be investigated in the final application.
For a smooth DC input voltage, the produced leakage current is less than 100 µA.
