DC input
The input can be powered from batteries or similar DC sources and must be a PELV or SELV source or an "Isolated Secondary Circuit" in order to maintain a SELV or PELV output.
DC input
DC input
Nom.
DC 48 V
+/- 25 %
DC input range
36-60 Vdc
Allowed voltage between input and ground
Max.
60 Vdc or 42.2 Vac
according to IEC 62477-1
Allowed input ripple voltage
Max.
10 Vpp
In the frequency range from 47 to 500 Hz, the momentary input voltage must always be within the specified limits.
Turn-on voltage
Typ.
35 Vdc
Steady-state value, see Fig. “Input voltage range”
Shut-down voltage
Typ.
32 Vdc
Input current
Typ.
5.4 A
For 48 Vdc input and 24 V, 10 A output load, see fig. "Input current vs. Output load"
7.5 A
For 36 Vdc input and 24 V, 10 A output load, see fig. "Input current vs. Output load"
Inrush delay
Typ.
200 ms
See Fig. “Input voltage range”
Rise time
Typ.
150 ms
At 24 V, 10 A constant current load, 0 mF load capacitance, see Fig. “Turn-on behavior, definitions”
250 ms
At 24 V, 10 A constant current load, 5 mF load capacitance, see Fig. “Turn-on behavior, definitions”
Turn-on overshoot
Max.
500 mV
See Fig. “Turn-on behavior, definitions”
Input capacitance
Typ.
1,650 µF
Installed inside the device, external capacitors on the input are allowed without any limitations.
Ext. input protection
See recommendations in chapter “Further notes on installation requirements”
DC input 1:Fig.1: Input voltage range, Turn-on behavior, definitions
DC input 2:Fig.2: Input current vs. output load
Requirements for the Supplying Source
In certain circumstances, the input filter of the DC/DC converter can show a resonant effect which is caused by the supplying network. Especially when additional external input filters are utilized, a superimposed AC voltage can be generated on the input terminals of the DC/DC converter which might cause a malfunction of the unit. Therefore, additional input filters are not recommended. To avoid the resonant effects, the minimal resistance of the supplying network which depends on the inductance of the input network, shall be above the boundary curve in Fig. “External input filter requirements to avoid filter instabilities”.
DC input 3:Fig.3: External input filter requirements to avoid filter instabilities