Output
The output provides a SELV/PELV nominal voltage, which is electrically isolated from the input voltage and is designed to supply any kind of loads, including unlimited capacitive and inductive loads.
The output is electronically protected against overload, no-load and short-circuits. In case of a protection event, audible noise may occur.
Output voltage
Nom.
24 V
Adjustment range
Min.
24-28 V
Max.
30 V
This is the maximum output voltage that can occur
at the clockwise end position of the potentiometer due to tolerances. It is not guaranteed value which can be achieved.
Factory setting
24.1 V
±0.2%, at full load, cold unit
Line regulation
Max.
25 mV
Between 18 and 35 Vdc input voltage variation
Load regulation
Max.
100 mV
In single mode: static value, between 0 and 10 A,
Typ.
1000 mV
In parallel mode: static value, between 0 and 10 A,
Residual ripple and ripple voltage
Max.
50 mVpp
Bandwidth 20 Hz to 20 MHz, 50 Ohm
Output current
Nom.
12 A
At 24 V and an ambient temperature below 45 °C
Nom.
10 A
At 24 V and an ambient temperature below 60 °C
Nom.
7.5 A
At 24 V and 70 °C ambient temperature
Nom.
10.3 A1)
At 28 V and an ambient temperature below 45 °C
Nom.
8.6 A
At 28 V and 60 °C, with an ambient temperature below 60 °C
Nom.
6.4 A
At 28 V and 70 °C ambient temperature
Overload behavior
Continuous current
Overload/ short-circuit current
Min.
15 A
Continuous current
Typ. Load impedance 100 mOhm
Output capacitance
Typ.
4 500 μF
Included in the power supply
Back-feeding loads
Max.
35 V
The unit is resistant and does not show malfunctioning when a load feeds back voltage to the power supply. It does not matter whether the power supply is switched on or off. The absorbed energy can be calculated using the built-in, large-size output capacitor.
Output 1:
Fig.5: Output voltage vs. output current at 24 Vdc input voltage, typ.,
Current limitation vs. input voltage, (23 V constant voltage load), typ.