Front side and operating elements

Front side and operating elements 1:
PS3031-4820-0000, front

Input terminals (screw terminals)

Designation (A)

Description

L1, L2, L3

Mains input L1, L2, L3

Front side and operating elements 2:

PE input (protective conductor)

Output terminals (screw terminals, two contact pins per pole)

Designation (B)

Description

+

two identical positive poles, positive output

-

two identical negative poles, negative output

DC-OK relay contact (spring-loaded terminals)

Designation (C)

Description

13 / 14 make contact

The DC-OK relay contact is synchronized with the DC-OK LED
See chapter on DC OK relay contact for more information.

Potentiometer for the output voltage

Designation (D)

Description

Potentiometer cover

Open the flap to adjust the output voltage.
Factory setting: 48.0 V at rated output current, "Single Use" mode

Overload LED

Designation (E)

Description

LED red

On when the voltage at the output terminals is <90% of the set output voltage, or in the event of a short circuit in the output.

Flashes when the switch-off has been activated or when the device has switched off due to overtemperature.

The input voltage is always required.

DC-OK LED

Designation (F)

Description

LED green

On when the voltage at the output terminals is >90% of the set output voltage.

Shutdown input

Designation (G)

Description

Shutdown input

Input for shutdown and remote control
Enables the power supply to be switched off. Can be activated by a switch contact or external voltage. The remote control input allows the output voltage to be set. For details see chapters DC-OK relay contact and Shutdown input

Selector switch for "Parallel Use" / "Single Use" mode

Designation (H)

Description

Selector switch for "Parallel Use" / "Single Use" mode

Set the jumper to "Parallel Use" mode if power supplies are connected in parallel to increase the output power. In order to distribute the load current between the individual power supplies, "Parallel Use" mode regulates the output voltage so that the idle voltage is approx. 4% higher than at nominal load. See also chapter "Parallel Use" for power increase. A missing jumper corresponds to "Single Use" mode.

LED displays

Overload LED

DC-OK LED

DC-OK contact

Normal mode

OFF

ON

Closed

During extra power

OFF

ON

Closed

Overload (Vout < 90%)

ON

OFF

Open

Short circuit at output

ON

OFF

Open

Temperature switch-off

flashes

OFF

Open

Shutdown input active

flashes

OFF

Open

No input power

OFF

OFF

Open